Instrument air backup control

Instrument air backup control

Instrument air backup control

(OP)
Hi all,

My question is about the more appropiate method to control the instrument air backup.

The instrument air is normally generated in the IA package and flows towards the IA header of the unit. In case there is a problem in the generation package, there is a backup from the IA refinery header. The two possible options are:

1) Installing a pressure control valve in the backup line. The pressure will be measured in the unit header. If the header pressure falls under 5 Kg/cm2 g the pressure valve starts opening and tries to control the header pressure with the refinery header air. When the generation package is recovered the header pressure rises and the backup valve closes.

2) Installing an on-off valve in the backup line with a solenoid. A pressure switch will be installed in the generation package outlet, so when the pressure falls under 5 Kg/cm2g the valve opens allowing the refinery header air in. When the pressure in the generation package is recovered the on-off valve is closed.

Thank you all of you for your help!

RE: Instrument air backup control

I prefer a modified 2).  Instal an on-off valve in the backup line with a solenoid. I prefer a transmitter to a control system that operates the solenoid on logic.  A pressure switch will work but is less reliable than a transmitter.  Further it is hard to detect the switch failure and easy to detect the transmitter failure.

RE: Instrument air backup control

(OP)
JLSegull thank you for your reply.

Let my expose you another option in order to get your opinion.

A control valve in the backup line with the pressure controller set at 5 Kg/cm2 g (normal instrument air header pressure is 7 Kg/cm2 g). When the pressure falls into 5 Kg/cm2 g the pressure controller opens 50% of the control valve travel and then it tries to control the pressure at 5 Kg/cm2 g. We do so because maybe the pressure control loop is not fast enough to mantain the header pressure.

We think that the problem with the on-off valve is that if the refinery instrument air header pressure is very high, our system may be damaged with the valve fully opened. Another possibility is that if the valve is fully opened and there is a problem in our instrumen air system we may demand so much air from the refinery header that we could trip the refinery instrument air package.

Thank you for your help!

RE: Instrument air backup control

Depending upon the volume and pressures, perhaps a self-contained pressure regulator could work.  Just set the regulator setpoint near the minimum pressure.  You could use the pressure transmitter and a control valve to work in a similar manner.  The setpoint for the "makeup air" could be near the minimum for the system.

The pressure reducing valve would be desirable anyway if the pressure from the refinery is too high.  You could have the on-off valve downstream of the regulator for the pressure reduction.

Many options exist that will work well.  Reading it again now I am not so fond of my earlier recommendation.

RE: Instrument air backup control

A self contained regulator on the back-up line is the most cost effective, and VERY reliable method.  Used through-out the industry for this service.  But an upgrade if you like would be to user a transmitter controlling a control valve.  Question you would then have is which way to fail the valve on failure (and no I do not mean air failure, but I mean on control signal failure).  Regulators you do not have this issue.  Given you HP back-up air supply I would fail last, but thats me.

Another thought on your solenoid idea (if you really like that) is to use a downstream orifice to cut any flowing pressure.  (I would assuem once the header got back to pressure and the header starts to "not flow" (i.e. pressure on each side of orifice starts to equalize) that the solenoid would close the valve.

Scott Hoffman
Mustang Engineering

RE: Instrument air backup control

(OP)
We haven't think about a self-contained regulator but it seems to be a very good solution.

Thank you very much!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources