3 Phase Generator on Single Phase Service
3 Phase Generator on Single Phase Service
(OP)
I have a 50kW 3 Phase 120/240 12 Wire Synchronous hydro generator which I want to install at a site that only has single phase service available from the utility.
Has anyone done something like this in the past? Can the machince be de-rated to a safe level and run with only one phase connected? At what level will the unbalance cause damage to the generator?
Has anyone done something like this in the past? Can the machince be de-rated to a safe level and run with only one phase connected? At what level will the unbalance cause damage to the generator?






RE: 3 Phase Generator on Single Phase Service
Properly connected, 2/3 of the original KVA rating. Typically the KW will equal the KVA with an allowable PF of 100%
Search this site.
This topic has ben covered extensively here in the last few months.
If you still have questions, by all means ask, but please do some research first.
yours