Induction Generator Negative Sequence Current Trip

Induction Generator Negative Sequence Current Trip

Induction Generator Negative Sequence Current Trip

(OP)
We have a 256 kW, 600 V induction generator coupled to a hydro turbine. We also have a 120 kVAR capacitor bank which switches in step after the generator in online. The unit is connected to a relatively small residential utility distribution system via a 600/4160 volt step up transformer (HV grounded wye - LV ungrounded delta).

Recently, after the unit was briefly shutdown for some mechanical work, the generator began tripping on negative sequence timed overcurrent (pick up set to 40 amps)at higher loads. LV system ph-ph voltages range from 601 to 608 when the unit is online. We are seeing a 12% current imbalance from the generator to the grid (capacitor currents only have a 4% unbalance).

Can any one give me a typical unbalance trip setting for an induction machine such as this? Could this possibly be a problem with the windings in the generator?

RE: Induction Generator Negative Sequence Current Trip

Sounds like your load is unbalanced. That wouldn't be unusual for a small residential system. Can you provide more description of your system. Is the generator operating in parallel with another source?

Consult the turbine-generator manufacturer for maximum tolerable unbalance and recommended trip settings.

RE: Induction Generator Negative Sequence Current Trip

You said induction generator. What is the other source? Have you measured the load currents when operating from that source alone?

RE: Induction Generator Negative Sequence Current Trip

(OP)
The other source is a utility distribution transformer with I believe a 25 kV secondary (I am not sure of the size or loading). The generator step up transformer is connected to the secondary of a 4160 volt distribution transformer which services a small apartment building. It is likely that due to primarily single phase loads which vary seasonaly that the loading unbalance (and voltage unbalance) will vary. I will consult with the generator manufacturer as to a recommended tolerance for unbalanced loading.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources