220kV GIS (Indoor) - Earth grid design

220kV GIS (Indoor) - Earth grid design

220kV GIS (Indoor) - Earth grid design

(OP)
GIS occupies much less space when compared with AIS. While this makes it desirable in places where the space is at a premium, it poses a challenge when it comes to designing the earth grid for the installation.
The location is with high soil resistivity and would it be advisable to embed the grid in the floor concrete to take advantage of the decreased resistivity!
Appreciate any advice / references.

Thanks

RE: 220kV GIS (Indoor) - Earth grid design

the resistivity of earthing system should be less than 1 ohm,embiding it in the concrete floor are subjected to many variables,i suggest to add some salts to the earthing rods in the yard to obtain the required resistivity

RE: 220kV GIS (Indoor) - Earth grid design

(OP)
Thank raadhatab for the opinion. I am afraid that it is not adequate for the indoor GIS with limited space available (treated earth pits are used widely otherwise).

RE: 220kV GIS (Indoor) - Earth grid design

Investigate if the following may be feasible to consider:

* Specify long ground rods
* Use diagonal counterpoises.
* Reduce soil resistivity with soil enhancement.
* Use the concrete and rebar as supplementary ground electrode.
* Interconnect ground grid if any close grid (Pwr plant, substation, etc.).
* Use the injected current to ground instead the full SC current.

RE: 220kV GIS (Indoor) - Earth grid design

Although Earth Grid should be designed to carry full short circuit current for 3 sec yet step and touch potential should be calculated based on max single phase ground fault current at the location keeping in mind appropriate  appropriated distribution factor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources