I'm currently investigate the effect of transformer in-rush current at a distribution level.  Need to know what instigate this behavior and its effect on the system.  If you know any source/websites for which I could study about this phenomenon, it would be very helpful.  Thanks, and have a great day.

RE: Transformer in-rush current at distribution level

Transformer inrush is based on the lack of back-emf (or counter-emf) upon energizing the primary winding. This results in currents which IEEE 242 recommends plotting at 10-12x the FLA for 0.1s, which is typically the worst-case. Once energized, the current reduces to the energization current plus the load current and losses.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources