Transformer Protection

Transformer Protection

Transformer Protection

(OP)
Dear All,
in a transformer protection graph with a fuse.
I have seen in most cases that transformr damage curve crosses fuse curve around 50 sec.

What's the concept behind this?
I have reviewd some articles,but couldn't find anything regarding this matter.

Thanks

RE: Transformer Protection

Because that's the best a fuse can do while still allowing you to energize the transformer.  It isn't because they want the curves to cross - just a fundamental limitation of trying to protect transformers with fuses.  

RE: Transformer Protection

Per IEEE 242, this is acceptable, since the primary fuse is designed to protect the transformer from faults (the lower/high current part of the damage curve), while still allowing inrush (typically 10-12x FLA for 0.1s). The secondary device should be set up to protect from an overload (the upper/low current part of the curve).

RE: Transformer Protection

(OP)
Thank you for all answers. We are going to change a 2000KVa, oil-filled transformer with a 1500KVA transformer, to my understanding since both size transformers are in same category and load or secondary or primary cables are not changing, the secondary relay settings also should not change.

A colleague suggested changing the breaker trip setting to 2000A from 3000A and so we need to change the CT ratio too!

I appreciate your feedback on this.




RE: Transformer Protection

Humble2000, I wouldn't be so sure about not having to change the secondary protection settings when going from a 2000kVA to a 1500kVA transformer. The damage curve will change, as will the overcurrent protection requirements.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources