Hello,
   I currently have a european machine that has 2 touch buttons(Palm Buttons)made by Allen Bradley that activate a cycle.This touch button has a 5 pin qd connector the pins are as follows.
pin 1 Positive DC wire
pin 2 N.C white wire
pin 3 Negative DC wire
pin 4 N.O black wire
pin 5 (Common)

This sensor puts out a 3 Amp 24DC Output

The PLC is a PNP.The signal comes through Pin 4.
This Palm button signal is a electromechanical relay.I have found high failure rate on these switches.So I investigated.I found this switch is rated for 200,000 cycles.I have exceeded this in 6 months of operation.So I purchase a Allen Bradley touch button(same series) with a solid state output.Rated for 50 million cycles.The only difference in pin configuration was there was no pin 5 (Common)on the solid state output ab switch.The other difference was the Output signal on the solid state switch.It was 800ma 24DC .I figured since the plc was still recieving the +DC input it would be fine.I figured pin 5 was just a european grounding difference.It had no relation to the PLC receiving it's input.I was wrong.The new Transitor switch powers up and says that it is giving a output as shown to me on the touch button indicator.The PLC however does not show a input on the controller.I did not have a meter ready so I could not test for voltage.Upon Investigation I found that Pin 5 on the "old mechanical relay switch" that on the switch itself said Common  was supplied by a branch of + DC circuit.So I dissconnected Pin five wire on the "old mechanical relay switch and I got the same results as the solid state switch.
  My question is is what is pin 5 Doing that I am missing.I do not think it is PLC related 3A DC output on the old switch versus 800ma Output Dc on the new transitor switch.I proved this out by disconnecting pin 5 from the branch dc circuit on the old switch with same results.I have contacted Allen Bradley on this issue and followed up but still no response??
     Thanks,
        Servo

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources