Plate & Frame install w/out VFD on Cooling tower and freezing

Plate & Frame install w/out VFD on Cooling tower and freezing

Plate & Frame install w/out VFD on Cooling tower and freezing

(OP)
I am involved in the install and operation of a P&F utilizing a closed circuit cooling tower.My supervisor is convinced we do not need a VFD on the cooling tower for winter operation.
 Since this is located in Colorado I am concerned that operating the plate and frame during cold ( below 32 deg F)weather will not be possible.
   As we do not have the ability to reverse the fans, will I have continual problems with freezing the louvers in the cooling tower making the P&F operation not an option? My supervisor also decided not to involve an engineer in the design and install of the P&F.
We have 19% glycol in the system,and this system cools a data center. Thanks for you help.

RE: Plate & Frame install w/out VFD on Cooling tower and freezing

19% by volume sounds low for your area. I think you should be about 45 to 50%. If you have a fluid cooler by-pass valve, then you would not need a VFD on the fan. Why the P&F in the first place, most free cooling data units are designed for glycol. Liebert has a few good sizing documents. The Liebert fluid coolers have multiple prop. fans all staged on LWT.

RE: Plate & Frame install w/out VFD on Cooling tower and freezing

(OP)
The main reason for the P& F addition is that we have two carrier model # 19XRV3032351CLH64 400 ton chillers that currently operate 24/7,primarily for the data center in the winter and I have two roof top units with a chilled water coils that  use the chilled water in the summer and economizer mode in the winter,with the chilled water loop operating at above 55 deg F to the RTU's.I am located in Denver,Colorado.The Lieberts in the data center are cooled with the chilled water loop. I only have one chiller running at any time and in the winter it operates at about 25%.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources