Helloeverybody, I received yesterday an asincronous generator on my office, and It`s comes with the neutral cable burnst.
  This generator is from an hydro unit, and the nameplate is 750 Kw, 1000 rpm, 380 V. This is the only problem, the cable that conects the star point with the terminal to ground is burnst.
  On my opinion:
  - Maybe we got a third harmonic problem.
  - Maybe we got a severe unbalance.

   There isn`t trend of the currents or some else information. This is a plant that have no so good control.

   Please, could somebody tell me if there is other causes that could cause this problem, and how can I avoid it, at this moment I´m thinking about multiply for 2,5 the nominal size.

   thank in advance

RE: neutral cable burnst on asincronous generator

I would suspect a bad connection. Over the years the most common cause of burnt cables that I have seen has been poor connections (high resistance, dirty, corroded).
respectfully

RE: neutral cable burnst on asincronous generator

waross is probably correct. however, it might be worthwhile to have a look through IEEE C62.92-1989 IEEE Guide to Neutral Grounding in Electrical Utility Systems - Part II - Synchronous Generator Systems to educate yourself on neutral grounding and synchronous machines.

RE: neutral cable burnst on asincronous generator

The neutral-earth bond is burnt? Then you have current circulating in your earthing system. This is a code violation in most places. The likely cause is you've got the neutral grounded at two locations, and current which should be flowing in the neutral conductor is actually flowing in both the neutral and through the earthing system. The ratio between the two currents depends on the relative impedances of the two paths.

You should ground the neutral at one, and only one location.

----------------------------------
  Sometimes I only open my mouth to swap feet...

RE: neutral cable burnst on asincronous generator

If it is a single unit of Power source I Suspect you had  bad connection ,which burned by  severe ground fault in system.
I my opinion (opinion only ) faults while in a  synchronised system  may result the same situation  if the weakest point( Bad Connection ) was neutral- Ground  connection and protections failed or insufficient.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources