3 Phase motor efficiency calculation
Hi
Can I calculate the efficiency of a 3 phase motor using the formula W= ?3 x V x I x PF x efficiency.
I have the Input power=1600 Watts, Input Voltage=460 Volts, Rated Current= 2.6 Amps and the Power Factor=0.85. Can I use the values to calculate the efficiency?
Looking forward to the reply
KShora
KShora
RE: 3 Phase motor efficiency calculation
Po(power out)
Pi(power in)
E=Po/Pi
thus, if you have the rating of the power delivered you just divide it and get your efficiency
OR can use the following
E=(746*HP)/[(746*HP)+(watts lost)] Where 746 is a constant and HP=horsepower
just my two humble cents, hope this helps
Your input power of 1600 W doesn't match the current, voltage, and power factor data you gave. That comes out to 1760 kW.
I don't have the Watt Loss data.
Does the equation I posted earlier make sense or not?
Gunnar Englund
www.gke.org
The power value that I have mentioned is written on the motor name plate, I suppose you are correct, it should be called as Output power.
Am I correct?
In case you have been waiting for someone to state this more directly, I believe that the posts above confirm that you calculate input power using W = sqrt(3) X V X I X PF and Efficiency = output Power / input Power. We assume that the 1600 Watts marked on the nameplate is output power and efficiency = 91%.
You may refer to IEEE Std 112-1996 IEEE Standard Test Procedure for Polyphase Induction Motors and Generators. Or you may refer to the ieee colorbook.
Or you may try this:
"ProMot, a decision support tool, is being developed within the framework of a project cofinanced by SAVE, aiming to aid end-users to explore the possibility of energy savings, in motor systems of an industrial or tertiary installation: electric motors, pumps, compressed air system and chillers. The tool helps in auditing an installation and performing simple meaningful calculations of purchasing, replacing existing or retrofitting electric motor systems. These technical and economic calculations are based on equipment data retrieved from widely accepted and regularly updated European databases and methodologies."
Download at this link,
http://promot.cres.gr/promot_plone/downloads/tools
bill
Power in = SQRT(3)*V*I*PF = 1.732*460*2.6*0.85 = 1760.8 Watts
Power out (on the shaft) = 1600 Watts (per nameplate data)
EFF = Pout/Pin = 1600/1760 = 0.9086 pu
And the total motor losses = Pin-Pout = 160.8 Watts