Dear All,

If the cable has neutral conductor, is the zero sequence impedance calculated different?.I have difficulty figuring out how the consultant has come up with the Z(on) at the end.

PRIMARY SUPPLY SYSTEM

Z0    0.586    <    82.88    100    MVA
    0.0726    +j    0.5812    100    MVA

SUPPLY TRANSFORMER

Primary Voltage      44    KV
Secondary Voltage .6    KV
ONAN Rating      2.5    MVA
Ratio  X/R      9.846    [typical]
Impedance      5.65%    on base

Include tolerance    -7.50%    [MIN]    
    5.226%    <    84.20    
Zmin=0.528%+j5.200%
    0.2112+j2.080    
                                
600    V CABLES    
750    MCM Cu        
14.9352    m RUN LENGTH    
49    ft RUN LENGTH    
6    CONDUCTOR/PHASE
6    NEUTRAL CONDUCTOR

Z 0=    0.05689    +j    0.60363    ? per mi        
=    0.00053    +j    0.00560    ? actual        
=    0.14665    +j    1.55607    ? on    
=    1.56297    <    84.62    ? p.u.         

Z(on)=.38990+j3.89204
Max Line to ground  =33200A

RE: Zero Sequence Impedance

Yes the zero sequence impedance is different with or without ground wire since is direct related with the neutral and ground return.

RE: Zero Sequence Impedance

(OP)
Thanks Cucky2000. I checked your graph webpage,didn't find any info about the subject( great graphs!)

Zn0=.14665+.2112+.0726=.43045
compare to Zn0=.38990

So, where the difference is come from?
I really appreciate, if you know any literature source on the subject that I can read

RE: Zero Sequence Impedance

(OP)
I appreciate any further reply on the subject issue.

RE: Zero Sequence Impedance

Zero sequence impedance of conductors in raceway is difficult to calculate accurately. Analytical calculations are not very helpful unless the geometry (number, spacing and lay of conductors) is consistent and type of raceway known.

Kerite has published some typical values for shielded cables.
http://www.kerite.com/catalog/catalogfiles/impedance_data_power.htm

RE: Zero Sequence Impedance

(OP)
In above calculation the cable zero sequence is given; however I don't get the same result when I add all zero sequence impedances together as the final result.
It seems having neutral conductor has some effects on conductor zero sequence.

Zn0=.14665+.2112+.0726=.43045
compare to Zn0=.38990

I appreciate if you could go through the calculations and see if you will get the same results or not.

RE: Zero Sequence Impedance

I'm not following his math either.
It appears we're assuming the transf. is connected Dy?

RE: Zero Sequence Impedance

Meant to say 'It appears we're assuming the transf. is connected YG-YG?'

RE: Zero Sequence Impedance

(OP)
No! Transformer is Delta-Wye.
Cables are inside PVC ducts

6X(4-750 MCM + 500 MCM GND)

RE: Zero Sequence Impedance

It's difficult to figure out what your calculations mean.

Quote:

PRIMARY SUPPLY SYSTEM

Z0    0.586    <    82.88    100    MVA
    0.0726    +j    0.5812    100    MVA

What are the two values?

Quote:

Z 0=    0.05689    +j    0.60363    ? per mi        
=    0.00053    +j    0.00560    ? actual        
=    0.14665    +j    1.55607    ? on    
=    1.56297    <    84.62    ? p.u.  

What do these four lines mean?

RE: Zero Sequence Impedance

(OP)
Sorry for bad representation of equations.

Z0=.586<82.88 This value is provided by the utility.
Z0= .586*cos(82.88)+j*.586*sin(82.88)

The second line is for cable based on 49' run

Z(49')=.00053+j.00560
Per unit value for 600V,100MVA
Z0=.14665+j1.55607
Z0=sqrt((.14665^2)+(1.55607^2))<atan(1.55607/.14665)
Z0=1.5629<84.62


RE: Zero Sequence Impedance

The primary Z0 should not be included if the transformer is D-YG.

I think I understand the impedance representations, but I agree it seems to not add up. Excluding the primary, I get:

0.358 + j3.636 pu

RE: Zero Sequence Impedance

Could the consultant be using a different MVA base?  The answer would be close if the base used was 75 MVA.  I can't think of a reason to do this.  How does the consultant's fault current calculation compare with yours?

RE: Zero Sequence Impedance

Z0 = 0.586<82.88°, which equals 0.07263 + j0.58148

Z0(49') = (0.05689 + j0.60363)(5280/49) = 0.00052795 + j0.00560187, which equals 0.00562669<84.616°

Z0(49')pu = (0.00052795 + j0.00560187)/(600V^2/100000000) = 1.56297<84.616° which equals 0.14665 = j1.556075

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources