Ssafety valve Installation

Ssafety valve Installation

Ssafety valve Installation

(OP)
I need to install two safety valves on my bioler, but the valves are to be installed to a single vent pipe using a Y connection. I need your advice

RE: Ssafety valve Installation

omerada,

Ordinary power piping code recommends individual vent line for each safety valve outlet.  It allows combined single vent line with requirement that the combined vent single line size have flow area equal or greater than the sum of the individual vent lines.  Each individual vent line would have been sized to be equal or greater than the outlet of each safety valve for adequate flow from each safety valve.

Not sure about any different nuclear piping code requirement, if it would be a closed vent system to a blowdown tank.  There could be some interaction between the safety valves discharging into vent line with backpressure, depending on the settings of the two safety valves.

If you are considering two safety valves mounted to same steam drum connection, then that would be another situation.

RE: Ssafety valve Installation

(OP)
This is actually a safety valve connection to our 150,000 lbs/hr boiler at 150 psi. I am just wondering if anyone has done this type of installation before so that I don't have to re-invent the wheel. I am concerned with any further calculations regarding some back pressure problems at the Y connection.

RE: Ssafety valve Installation

ApC2Kp is correct on the area part as a starting poit.  Typically, if the relief valves is a 8 x 10, then the two lines would join into 14" to be safe, but a 50' 14" line has 11 psi drop   and a 50' 12" line has 16 psi drop.  So a 12" would work for that distance.  A 10" line has a drop higher than 25% of the inlet pressure (this is just a quick analysis and not the final answer)

RE: Ssafety valve Installation

(OP)
Hello dcasto, the phrase " if the relief valves are 8 x 10,..." are you referring to the areas of the valves? The internal diameters of the valves are 4" each. Can you explain further please. The height of the vent line from the valve to the roof is about 100 feet.

RE: Ssafety valve Installation

8" inlet by 10" outlet.  I did a quick sizing and came up with a R orifice (16 in^2).  Looked up someones R orifice and saw a 8 X 10.

I then did some pressure drop calculation based on 300,000 lb/hr steam.

RE: Ssafety valve Installation

(OP)
Are there any relationship between the ASME BPVC Section III and API 520 and 521 as regards MAWP for relief devices. These bodies have different formulas for calculating the minimum discharge area of the relief valves, do they give the same results?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources