Spread monitor

Spread monitor

Spread monitor

(OP)
After how many days of GT operation can we start detecting Exhaust Temperature Spread

RE: Spread monitor

You should monitor those values during start-up and full speed/no load conditions.

Once the turbine is at load, the readings should stabilize after an hour or two (assuming no load swings).

RE: Spread monitor

the exhaust temperature spread monitor is enabled automatically in the logic.

during startup,acceleration and load selection the exhaust temperature spread monitor has a bias added to allow for transients.

if there is high spread at full speed (for instance if a can flames out) the unit will trip on high spread.

thermal stabilization of the unit has nothing to do with the spreads.
thermal stabilization of the unit is defined by the rate of change of the interstage temperatures (wheelspace thermocouples), usually: less than 2degF in 15min

high exhaust spread is related to combustion or exhaust thermocouple problems.

the unit could be in transient thermal state (wheelspace temperature changing) and still have a high spread condition and trip.
conversely... the unit could have high wheelspace temperatures (in alarm) due to damaged sealing and no spread.

saludos.
a.

RE: Spread monitor

Depends on the Unit.  Who's GT? What Type? Fuel Etc

RE: Spread monitor

How much spread are you talking about, and what are the specified limits on your turbine?

rmw

RE: Spread monitor

Your spread will likely change with load, and the position of the highest and lowest readings will also be affected due to the change in "swirl".  That is what I meant in an earlier post when I talked about allowing the readings to stabilize after a load change.

If a can flames out at no-load, put some load on it to increase the compressor discharge pressure.  This may be enough to allow the unit to cross-fire between cans and re-light the flame-out.

RE: Spread monitor

I think we need to know the GT type and manuafacturer.  Not all GT's even have cans. Until we know the type of GT any response is a shot in the dark.

RE: Spread monitor

agree with you GT startup... seems like caemaniac either lost interest or cannot find the nameplate :oP

saludos.
a.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources