shear strength of fiber reinforced concrete floor

shear strength of fiber reinforced concrete floor

shear strength of fiber reinforced concrete floor

(OP)
Hoping someone can help me here.  I'm trying to find some design standards/equations for allowable "Punching Shear" (i.e., two-way shear) on a 6-inch thick concrete floor that only has synthetic fiber reinforcement (uniformly dispersed).  Normally, I would follow the provisions of ACI 318.11.12.2 but this assumes that it is just "plain, unreinforced" concrete.

RE: shear strength of fiber reinforced concrete floor

The fibers do not add any significant structural strength to the slab.  There only purpose is crack control, i.e. holding the cracks together.

RE: shear strength of fiber reinforced concrete floor

Yes, what GeoPaveTraffic said.

RE: shear strength of fiber reinforced concrete floor

(OP)
Hmmmm, well ... I have a maximum service load of 21.6K (steel leg) sitting on this 6" floor ..... following ACI 318, Chap.22 (struct. "plain" concrete) with phi=0.65, fc=4000 psi, load factor of 1.4 ..... I get a minimum base plate req'mt of 8.5" x 8.5"; and the fiber reinf. does nothing to help me reduce the base plate size?

  The loading is from a series 38-ft high special rack/shelving system. The shelves come with a standard 4.5" x 4" base plate (6" x 6" plate is optional and extra).  The manufacturer/supplier also informed us they have never had a problem with this rack system on 6" concrete floors in the past.

All comments welcome ..... TIA (thanks in advance)

RE: shear strength of fiber reinforced concrete floor

I consider synthetic fibers to be one of the best (concrete) inventions "since sliced bread" and have been using them for various projects since 1985...
but for your situation I completely agree with GeoPaveTraffic and JAE - they won't help at all.

www.SlideRuleEra.net idea

RE: shear strength of fiber reinforced concrete floor

Think of it this way:

Fiber structural capacity = 0



RE: shear strength of fiber reinforced concrete floor

The loads are pretty high and depending on the soil and the leg spacing the slab should be checked for flexural tension.

The fibres, as I understand, helps with the retention of bleed water and the improvement is gained by a more uniform hydration of the concrete gel.

Dik

RE: shear strength of fiber reinforced concrete floor

Agree with dik that the loads seem high.  Flexural tension can be checked by the method shown in "Designing Floor Slabs On Grade" by Boyd C. Ringo and Robert B. Anderson, pages 43 to 45.

RE: shear strength of fiber reinforced concrete floor

Yup....what they said about fiber.  Remember fiber enhances the properties of concrete, but it doesn't reinforce it for anything other than creating a path break for cracking.

RE: shear strength of fiber reinforced concrete floor

If possible check the original content of the fiber.  If the floor has anywhere near 2-3 bags per cubic yard you can bet that shrinkage cracking is all that the fiber is for.

If, however, you find that there is significant amounts of fiber (5-7 bags) or greater than 0.5%-2% then perhaps you may have some residual strength but I bet you'll be hard pressed to find a text on mechanics that will provide the necessary and reliable strength.

Regards,
Qshake

Eng-Tips Forums:Real Solutions for Real Problems Really Quick.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources