200-500kw generator protection settings
200-500kw generator protection settings
(OP)
Dears,
Can you please tell me recommendations about settings of over/under voltage, frequency and earth fault settings for 200-500 kw generator sets, driven by diesel/gas engnines.
Can you please tell me recommendations about settings of over/under voltage, frequency and earth fault settings for 200-500 kw generator sets, driven by diesel/gas engnines.






RE: 200-500kw generator protection settings
Can you please help me to find out any standard information about setting of these protections
RE: 200-500kw generator protection settings
C37.101-1993 IEEE Guide for Generator Ground Protection
C37.102-1995 (R2001) IEEE Guide for AC Generator Protection
From IEEE at ieee.org. N.B.: online are DESCRIPTIONS of standards, and NOT the text of the standard itself. You can generally purchase standards on line, so they’re rarely free. Time to get out your credit card.
RE: 200-500kw generator protection settings
RE: 200-500kw generator protection settings
www.geindustrial.com/pm
www.selinc.com
www.basler.com
www.beckwithelectic.com