on a rslogix micrologix 1000 plc, what is the address
for the function to flicker alarm light?
Thanks....
for the function to flicker alarm light?
Thanks....
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
STATUS BITS FOR ALARM PILOT LIGHTS
|
RE: STATUS BITS FOR ALARM PILOT LIGHTS
Application note: You can write any value to S:4. It will begin incrementing from this value. You can use any individual bit of this word in your user program as a 50% duty cycle clock bit. Clock rates for S:4/0 to S:4/15 are: 20, 40, 80, 160, 320, 640, 1280, 2560, 5120, 10240, 20480, 40960, 81920, 163840, 327680, and 655360 ms The application using the bit must be evaluated at a rate more than two times faster than the clock rate of the bit.
RSLogix 500 - Copyright Rockwell Software 2000, 2001, 2002
So....
S:4/5 O:1/0
-] [----------( )-
O:1/0 would be on for .64 seconds and off for .64 seconds
RE: STATUS BITS FOR ALARM PILOT LIGHTS
All the detailed information is very much appreciated.
I am new at this forum, any forum for that matter.
I am glad to see all the smart minds coming together
and helping everyone out.
I went ahead and completed my program..
Alarm is FLASHING VERY WELL............
Thanks,
PLCROOKIE............ CALIFORNIA.