Reverse Reactive Power Problems
I have been researching this subject and to date have come up with no real definitive answers or solutions. I have been reading the site for some time and thought this might be the place to start.
I am looking after a marine plant consisting of two 670kva alternators and two 1600kva alternators, all driven by diesel prime movers, the larger being Caterpillar and the smaller MTU engines. The main consumer is a 3MW motor drive frequency converter, six pulse to the network with 4 branches of 5th Harmonic filters connected dependent on output of the main drives. Bus network is 690V. This is a new installation and intially it appeared to function ok, but it has recently shown a few serious faults.
Basically, when the main drive is engaged, the harmonic filter is engaged to the network, and whilst running the larger gensets with the main frequency drive there is no apparent problems. However, as the load is increased and a smaller generator is paralleled, active load sharing will take place and then appears to stop at say 50% of the running engine. After 30 seconds or so this will then trip off line, the DEIF PPU control for the generator gives the alarm for 'reverse reactive power'(var import). This fault occurs regardless of engine combination, but always when the smaller sets are joining a larger set or sets. There is no problems connecting the smaller engines if the load on the motor drive is reduced below 30%. It appears from my limited experience that the affect of the harmonic filter is to draw the smaller sets into a 'leading power factor' scenario, and hence the trip is real and not nuisance as the designers insist.
The DEIF unit is controlling Reactive load sharing, the proposal is to disconnect this feature. It is apparent that this problem disappears when the Harmonic filters are switched off, i.e syncrohnising and sharing is not a problem at any load, and no trips occur in any configuration.
My question is does anyone have any experience of this in similar installation, and is this a design issue as it has 'technically' never been proven to work in this installation to date. I have long said that the Harmonic filter should have been installed to protect low end consumers (in the 440v network) rather than on the main 690v distribution, as it appears on the surface that the smaller sets are unable to cope with the reactive power generated when the Harmonic filters are on line, despite the fact that this is under the generators load reactance curve.
Many thanks.
RE: Reverse Reactive Power Problems
Check out www.harmonicsolutions.co.uk they have a paper on there that references a similar problem on an offshore oil platform.
Many thanks for your response, I have been looking around for a company like this for some time now as I have a fair few THD issues to solve as well!
I have actually read this report previously, it does not quite address all the problems we are experiencing here. This is the first time I have ever seen the reverse reactive power device activate and cause a disconnection.
Short answer is turn off harmonic filters. If harmonics are not a problem without the filters why have them? Excessive capacitive load is bad news for the generators. You need to involve people like Russelectric who knows generator controls (not even generator manufacturers themselves).
Trying to parallel units of different manufacturers and of diff rating is not easy. There may be some teaking required in setting of reactive load share and power factor control. Not sure how your sets are setup, they can be set for a fixed var or p.f. control. You may need upgrading the AVR to modern digital AVRs. Old style analog AVR can not handle harmonic effects too well.
What control mode are your AVRs in? Are they designed to maintain constant voltage? Operating paralled sets all in voltage control could explain what you are seeing. Can you run the largest set in voltage control mode and the others in PF control? If so, set the small sets to either float VAr-neutral on the system with a unity PF, or to run at a slight lagging PF (VAr export) if possible.
What is the PF of the overall load?
  Sometimes I only open my mouth to swap feet...
Can you explain which units trip. Is it the smaller units?
One thing you should look at is whether the Deif units are set up so that each generator provides the same amount of kVAr or whether it is proportional to their ability to provide (ie pF control)
With mismatched sizes the only way is a percentage basis for kW and each hunting for the same pF. If you have AVRs that operate at a different rate then reverse VARs can be common as one AVR drives faster into the load, stripping the other of VArs. Usually it would be the smaller machine that would trip as the same percentage change for the larger is more VARs
Investigate the VAR control. Make it slow.