×
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Log In

Come Join Us!

Are you an
Engineering professional?
Join Eng-Tips Forums!
  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!
  • Students Click Here

*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Posting Guidelines

Promoting, selling, recruiting, coursework and thesis posting is forbidden.

Students Click Here

Jobs

Arc Flash & GE AK-50 Circuit Breaker

Arc Flash & GE AK-50 Circuit Breaker

Arc Flash & GE AK-50 Circuit Breaker

(OP)
I'm doing an arc flash study, and according to ETAP if I delay the LSIG settings and increase the pickup time on a GE AK-50 (1600A frame) breaker the arc flash will increase - the converse is true if I turn down both of the settings...

Somehow this does not seem correct to me? ie: The CPT of the breaker is still the same regardless of it's setting therefore wouldn't the arc flash still be the same? ie: The charging spring that opens the breaker still exerts the same force on the contacts and therefore it still takes the same amount of time to open the breaker...energy is proportional to contact parting time!

Can someone point me in a direction to clarify this? Does IEEE 1584-2000/2002 say anything about this?

RE: Arc Flash & GE AK-50 Circuit Breaker

The breaker is interrupting an arcing fault downstream of the breaker.  The arc flash energy is proportional to the total clearing time, so increasing the time for the breaker to start to open will certainly increase the amount of arc flash energy.

RE: Arc Flash & GE AK-50 Circuit Breaker

If you are thinking about a fault within this breaker, you have to look upstream for the protective device.

As David said, the program is using the clearing time for the breaker, in conjunction with the arcing current to determine arc-flash energy for faults downstream of the breaker, such as at the MCC it might be feeding.  If you slow down the LSIG, the arc lasts longer and energy is higher.  In 480V trip units, the breaker clearing time is built into the time current curves.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources