I have looked at a New Residential two-story home in PA. It has a CMU foundation with crawlspace and an attached garage w/frost walls to one side.
Details:
The crawlspace is about 5.5' tall with vapor barrier and crushed stone on top which is uneven and sparse (non-compacted).
Facing the house, the exterior grade at foundation varies (due to minor slope) with 36" above base of footing at left side foundation wall and 36" (left corner) to 60" (right corner) at front and rear walls. Garage is on right side.
Soils are clayey loam type.
No visible drainage pipe to daylight
No sump pump/pit in crawl nor was any moisture noted.
PA has adopted the 2003 IRC. 42" frostline footing depth required.
Situation:
Inside the crawlspace, the crushed stone is so sparse in many areas that the bottom edge of the footing is visible. The stone can easily be brushed away from the footing to the bottom edge inside the entire crawlspace.
Questions:
Is this a concern for lateral movement due to hydrostatic pressure or frost heave?
What are proper remedies, if needed, to prevent possible future cracking or inward foundation movement?
I do not believe seismic protection is required since this on the Northeastern state line.
Details:
The crawlspace is about 5.5' tall with vapor barrier and crushed stone on top which is uneven and sparse (non-compacted).
Facing the house, the exterior grade at foundation varies (due to minor slope) with 36" above base of footing at left side foundation wall and 36" (left corner) to 60" (right corner) at front and rear walls. Garage is on right side.
Soils are clayey loam type.
No visible drainage pipe to daylight
No sump pump/pit in crawl nor was any moisture noted.
PA has adopted the 2003 IRC. 42" frostline footing depth required.
Situation:
Inside the crawlspace, the crushed stone is so sparse in many areas that the bottom edge of the footing is visible. The stone can easily be brushed away from the footing to the bottom edge inside the entire crawlspace.
Questions:
Is this a concern for lateral movement due to hydrostatic pressure or frost heave?
What are proper remedies, if needed, to prevent possible future cracking or inward foundation movement?
I do not believe seismic protection is required since this on the Northeastern state line.






RE: Unsupported crawlspace footing
Is the crawl space heated? Again, makes a difference... And if it is heated, is it a reliable heating situation (ie: regularly used space) which is unlikely to be left unheated for more than 7 days?
Perhaps the outside wall was insulated with SM insulation? Very unlikely, but possible.
So as I see it you have two potential structural problems: Frost heave (as I believe you realize from your mentioning the min. frostline footing depth required) and the unrestrained footing against latteral thrust.
If I've understood and outlined your case correctly, there are a few possible solutions, but my number one choice would be to insulate with structural SM foam and finish the crawl space floor (ie: give it a slab).
B.Eng (Carleton)
Working in New Zealand, thinking of my snow covered home...
RE: Unsupported crawlspace footing
My answers to your questions in black.
BH.Eng Wrote:
Are the walls backfilled?
Yes
Is this crawl space below ground level, and as such properly a very rough basement area?
Yes, See the Detail: section of my original post as to height of grade/slope at this crawlspace foundation type.
This would be a more severe situation in that case, as the base of the footings must have either a slab to push against, or be burried in a sufficient amount of soil & gravel to resist thrust of the soil pressure on the outside.
There is absolutely no support at the entire interior side of this exposed footing. This was a flat excavation and footing forms were constructed/poured on top of flat surface, then finished with loose/sparse crushed stone inside the floor area. The Builder finished this project 6 months ago and the local building codes official signed off on this house. Builder stated to me that there was no intention of ever pouring a finish floor in this space and sees nothing wrong with it the way it is. I guess that's why he's just a builder!
Is the crawl space heated?
Yes, with a ceiling mounted space heater set at just enough to keep the plumbing from freezing
is it a reliable heating situation (ie: regularly used space)
Somewhat reliable, but would be unknown if unit was defective, since this area would have infrequent entry.
which is unlikely to be left unheated for more than 7 days?
It is possible to be unheated for 7 days or more but it is unknown what the lowest ambient temp could be reached assuming the heated living space above is still actively heated. We are in Zone 4 reaching temps of -3F (-17C), down to -30F (-34C) for a few days in a row.
Perhaps the outside wall was insulated with SM insulation? Very unlikely, but possible.
No Insulation outside or inside. Of course you knew that! It's typical of saving that almighty dollar!!!
So as I see it you have two potential structural problems: Frost heave (as I believe you realize from your mentioning the min. frostline footing depth required) and the unrestrained footing against latteral thrust.
Touche'. The reason of my posting here to confirm my initial thoughts.
If I've understood and outlined your case correctly, there are a few possible solutions, but my number one choice would be to insulate with structural SM foam and finish the crawl space floor (ie: give it a slab).
Which makes all the sense in the world. Thank you!
One more question if I may.
If the footings had rebar (twins) and block walls with pinned rod/grouted cavities every X amount of feet, would there still be a likelihood of cracks or movement? would this situation be acceptable?
RE: Unsupported crawlspace footing
Back to your actual question: IF reinforce footing as a horizontal beam and IF the masonry units were given a doweled shear connection into the footing, could it work? Yes, but I doubt that's what's been done. The design would be unusual, but not implausible. I would not design a structure like this, since you still need to have the horizontal beam be capable of spanning between perpendicular walls in case of EQ loads. Not a good solution, not a good construction.
Oh, and yes, unless the wall as well was reinforced with steel (or perhaps fibres) I would think that you're running a greater risk of cracking. Also, it would be absolutely essential to have PROPER backfill and big-O (drainage) right down at the base of the footing for this wall to work as constructed.
I would, having said all that, design a foundation/basement like this in one (and only one) situation: If it was on bedrock. Since you're on clay-loam and worried about frost-heave, I'm pretty sure I can set aside the bedrock idea...
One last thought: I've never heard of a forensic engineering expert who didn't insist that collapses (or non-catastrophic failures) are always due to a string of conditions, situation, occurances or coincidences. I would think that (bearing in mind I haven't actually seen your situation) what you have here is step one of a three, four or five degree of failure system.
Hope that helps,
Good luck,
YS
B.Eng (Carleton)
Working in New Zealand, thinking of my snow covered home...
RE: Unsupported crawlspace footing
Check one thing before calling for remedial works: You are laterally supported at the top and sides, with partial restraint at the bottom. Consider a yield-line solution for your walls with these conditions, and determine an appropriate moment capacity for your wall if the CMUs are nominally reinforced with your code's minimum vertical and horizontal steels. From that you can altually determine the maximum horizontal span permissible. Your walls are short, so that's going to be a big help.
Failing all of that, you can always present your client with the possibility of getting a Geotech's help for the lateral restraint of the footing... If it's effective with just a slight shear-key into the clayey loam, you've actually got a situation that works, if the wall is capable of restraining the backfill along it's 5.5' vertical span.
Again, good luck,
YS
B.Eng (Carleton)
Working in New Zealand, thinking of my snow covered home...
RE: Unsupported crawlspace footing
I agree with you it is doubted that special reinforcement design was in place for this ordinary residential construction.
Thanks again for insight on my follow-up questions. Lots of great information.
Igor Smetaniuk
Glen Spey, NY
RE: Unsupported crawlspace footing
Please let me know how it's turns out... And I don't think you're client is going to like the cost of the insulation!