Maximum allowable velocity in public water mains???

Maximum allowable velocity in public water mains???

Maximum allowable velocity in public water mains???

(OP)
I have a site with a several fire hydrants and a 50,000sf building on site and the client is requiring that the maximum allowable velocity in the site water lines be kept at 10fps or less.  Is this typical practice to use this as a limit for on site fire and water lines?

RE: Maximum allowable velocity in public water mains???

Its very typical for most all pipe flows where pressure drop over long lengths is of concern.  It also limits erosion from foreign particles being carried along with the flow.  Many projects also require a minimum velocity of 3 ft/sec to help in keeping foreign particles from settling and accumulating in low spots.  

The maximum velocity might be increased (if allowed by your project specs) over short lengths of pipe, near pumps or other equipment, as long as the pressure drop is tolerable.

One caution.  Approaching or exceeding 10 fps may increase the likelyhood of hydraulic surges.

BigInchworm-born in the trenches.
http://virtualpipeline.spaces.msn.com

RE: Maximum allowable velocity in public water mains???

From the military civil engineering guideline:

Try:www.usace.army.mil/inet/usace-docs/eng-manuals/em1110-1-4008/c-3.pdf


For normal liquid service applications, the acceptable ft velocity in pipes is 2.1 ± 0.9 m/s (7 ± 3 ft/s) with a maximum velocity limited to 2.1 m/s (7 ft/s) at piping discharge points including pump suction lines and drains. As stated, this velocity range is considered reasonable for normal applications. However, other limiting criteria
such as potential for erosion or pressure transient
conditions may overrule. In addition, other applications
may allow greater velocities based on general industry
practices; e.g., boiler feed water and petroleum liquids.

RE: Maximum allowable velocity in public water mains???

You may be interested also in various references in the past thread at http://www.eng-tips.com/viewthread.cfm?qid=132053 (it appears for whatever reason many authorities for get some nervous with certain piping materials at variable velocities beyond say 1 or 2 m/s (3-7 fps)).  

RE: Maximum allowable velocity in public water mains???

The Washington State Department of Health (DOH) recommends a maximum velocity of 8fps, but permits greater velocities during fire flow conditions.  This may be a way to address your concern.

"8.1.6    Maximum Velocity:
The DOH recommends that the design of distribution mains not exceed a maximum velocity of eight (8) feet per second (fps) under PHD conditions, unless otherwise specified by the pipe manufacturer.  Maximum velocities of greater than eight fps may occur under fire flow conditions, for short sections of mains, or for piping within pump and valve station facilities.  Long sections of mains with higher velocities should be checked for transient (water hammer) conditions.  Refer to Section 8.1.8 for discussion on surge control and Section 8.2.4 for modeling transient conditions." -http://www.doh.wa.gov/ehp/dw/DesignManual/chapter_8.DOC

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources