zero sequence generator
If the manufacture only provides positive sequence impedance for a 3 winding core type, 12/11/0.415kV transformer with out giving the zero sequence impedance, what approximation can I take?
Any links or doc that I can refer to will be very much appreciated.
RE: zero sequence generator
Depends on the connection (vector group) and which winding you are talking about.
Try a Google search for transformer symmetrical components.
wonderchi,
"..12/11/0.415kV transformer ... "
From the above voltages it sounds to me that you are in the IEC world.
Please refer to Table 1 of IEC 60076-8 for a complete list of typical zero sequence impedance values for 3-winding transformers with different connection symbols. But, if you are looking for an accurate value, the only contact is the transformer manufacturer.
Hope this helps.
Kiri