Eletrical Grounding

Eletrical Grounding

Eletrical Grounding

(OP)
I work in NYC I am a plumber and have allways seen the electrical service grounded to the water main. Now keep in mind I work in new construction high rise buildings I have gone to this new job and the electrical contractor will not give a reason why he has not bonded his service to the water main except citing re cent code changes now I have been in a few buildings since the changes here and all have there services bonded to the water main! I even fought with one contractor in 2 buildings about him trying to bond to the gas service can any one give me info because I feel this is a dangerous thing happening

RE: Eletrical Grounding

A connection from the main service disconnect ground bus to the water service (at a point no more than 5ft from the entrance to the building) is required by the National Electrical Code. I'll check my New York City code book on Monday.

A connection to gas piping is not required by any code to my knowledge.

RE: Eletrical Grounding

Without actually checking the code, I believe that the piping material enters the consideration.  Not much point grounding to a water main that is all plastic underground.

RE: Eletrical Grounding

(OP)
The water main is a six inch ductile iron main . And as far as the bonding to the gas service if we install a steel service line then we install anode bags on it to prevent grounding eating away at the pipe also when a steel gas service is installed two things are done one is a die-electric gasket and bolt kit is installed at the head of the service and the utiltiy company performs a voltage test on the main to insure it is insulated from the ground by shooting 30,000 volts if a section is not wrapped properly you see the sparks hit the soil I thank all of your information nycpipewelder

RE: Eletrical Grounding

250.104(B)requires all metallic piping likely to become energized, including gas, to be bonded.

RE: Eletrical Grounding

Stevenal - I had forgotten that requirement. Not sure I can think of a situation where gas piping would be 'likely to become energized'.

RE: Eletrical Grounding

"Not sure I can think of a situation where gas piping would be 'likely to become energized'."

Kitchen range with electric igniters, bathroom heater in steamy room used by wet barefoot people, etc.

RE: Eletrical Grounding

Absolutely true Itsmoked,

Things such as:
-Packaged Gas-Electric Air Conditioning units
-Gas Clothes Dryers
-Gas Barbeque with electric strike start
-Gas fired water heater connected to Jacuzzi/pool/Sitz bath pump systems
-Natural gas fired sterilizers in hospitals
-Commercial laundry tunnel washer/dryer systems
-Gas fired power generation equipment

There are numerous pieces of equipment where gas connectons and electrical connections enter adjacent to each other. This is very common in many healthcare, industrial and commercial facilities.

We always bond natural gas piping systems.  They are not used as a grounding electrode, they are just bonded to assure that should an accidental fault occur, there is a path to dissipate the energy.


RE: Eletrical Grounding

Interesting. I can't recall seeing bonding jumpers to gas piping and never specified it myself. Maybe it's time to re-evaluate.

I wouldn't have thought to consider that as likely to become energized because it seems to me in most cases the piping is effectively connected to the frame of the appliance via it's fittings. Is a bonding jumper always required? I don't do healthcare facilities, but could understand those having more stringent requirements.

RE: Eletrical Grounding

By my read of the code section, it seems that the ground wire for any of these electric/gas appliances may serve the function if sized properly. I once checked continuity from ground prong to gas connection on a gas dryer. It was continuous, even through the flexible gas hookup. In the end the AHJ decides.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources