IBC Handrail Extentions for Industial Stairs ?????
Hey brothers and sisters,
I have a question regarding the Handrail extentions called out in the IBC 2003 1009.11.5
I'm a structural engineer working for the contactor in this case, and the Design Engineer is insisting on these 2 ft handrail extentions in an purely Industrial building. These extentions are not practical, yet there are no exceptions in the code.
OSHA does not require these extentions in there "fixed industrial stair spec".
Since I am not a member of ICC I can not get a code interpratation, you got to pay for that.
Anybody out there run into this?
Also I'd like some clarification on the 7" riser and 11" tread requirement, again there is no exception for Industrial, yet OSHA has a range for riser and tread dimensions way outside this.
It seems common sense to me, IBC needs to add these excepetions. These requirment are clearly not intended to industial, platforms, catwalks and the like, but for "means of egress" only
RE: IBC Handrail Extentions for Industial Stairs ?????
Even so, my IBC 2003 shows a 12" extension in this section, not 2'.
You are right it is 12" per 1009.11.5.
And I agree with your reference to "means of egress"
The part that leads to some confusion is in 1607.7.1 were they list load exeption for Group F (Factory and Industrial) I would think they could do the same in Chapter 10. But I guess, like you said it is implied because mech access stairs are not "means of egress"
thanks for the imput.
I just would like something official, because this comes up alot when you deal with professionals that have mostly commercial/residential experience.
I also had a local plan reviewer flag the same thing on a mechanical access platform. He even quoted the IBC chapter 10.