Generator terminology
I am trying to differentiate between an ac generator power factor rating and the impedance of the generator to answer a specific question. If somebody is asking the impedance of a generator, what would they be looking for exactly.
RE: Generator terminology
There is no single "impedance" for a dynamic, non-linear system like a generator. For a single value, the most useful impedance is the sub-transient impedance (X"d).
I don't think there is much direct relationship between power factor rating and the impedance.
Suppose we have a 100kva generator. If we decide to rate it at 100% power factor, we must install a prime mover with a 100KW output (133 HP.)
If we decide to rate the generator at 80% power factor, the prime mover need only supply 80KW. (107 HP.)
The actual power factor depends on the load, not the generator.
respectfully
- the power factor of that generator gives an idea on how much reactive power it can produce.
- the Xd (this is, I assume, what they are really expecting when they ask for the 'impedance') gives an idea of how much reactive power it can absorb. If it is a multipole generator, you would need the Xq also.
Most important of the reactances, Subtransient reactance X"d, is useful to quickly find out the maximum short circuit current the generator can deliver.
For example, the maximum SCC a generator can deliver will be FLA/X"d.
A 600A rated generator with 0.15pu X"d (or 15%) will deliver 600/0.15=4000A. There are some other variables but their effect would not be significant.