HVAC problem

HVAC problem

HVAC problem

(OP)
I am involved in designing a very small hvac system with a Blower Fan at 700 CFM 2inwg. I can not find a sutible equation that will give me the preassure losses for the following:

A 700 CFM supply entering a 15" diameter cone diverging to a 8" diameter circular duct. The cone is 17" long with an angle of 10 degs.

B. A circular spilter duct to split the 700 cfm to 350 cfm to different directions.
If anyone have any Ideas Falcon1654 would appreciate it.

RE: HVAC problem

The loss coefficient in your case for the area ratio of 3.51 (=15*15/8*8) with 100 taper is about 2.56. The velocity at inlet condition is about 570 fpm. Now calculate velocity pressure at inlet condition and multiply it with the loss coefficient. This gives you pressure loss at the section.

Refer to ASHRAE duct fitting database or SMACNA manual for other data.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources