concrete failure along steel surface
Hi everyone; looking for some great tips on this one.
There has been a failure of a concrete bulkhead(headwall) at the mine where i work. The likely cause of this failure is from a loader dumping above this headwall and the vibrations travelling down thru the steel and into the concrete surrounding the steel.
I am advising for the existing concrete to all be chippped away, the rebar to be replaced and fresh concrete to be installed ( a basic reno job).
My questions are:
Is there a material that can be placed between the steel and concrete to dampen the vibrations. perhaps high density rubber or some form of structural insulation?
Also; how long should the concrete be left to cure before introducing it to vibration and stress?
thnks a bunch............
My questions are:
RE: concrete failure along steel surface
Your presumptive cause of failure does not seem plausible. The actions you have described result in low frequency vibrations. I suspect the magnitude of the load is more prominent as a cause than the vibrations that occur as a result of the load.
If you could describe the way the concrete failed it would be a bit more helpful.
Concrete transmits vibration, not just the steel. Yes, they transmit sound wave at different velocities, but both are fairly high, particularly with low frequencies. High frequency sound or vibration in concrete gets dispersed because of the voids and other discontinuities and path interruptions that occur in concrete, as high frequencies generally tend to have low amplitudes that can't "jump" the discontinuities.
How long has the structure been in place days / weeks / years??
Any nearby blasting with high peak particle velocities???
the machine that is dumping into the the hopper above the concrete headwall is a 988 loader; this is above ground inside of a building.
the concrete has just disintegrated; falling out onto the floor in large chunks. the concrete that is still in place is attached to the rebar that was used to reniforce the concrete.
if vibration isn't the problem perhaps the caocrete needs to be thickened to supply it with more mass to provide strength?
eli.
You need to realize that the loader weighs 110k without any attatchment or load. It will be very expensive to build the monument required to keep the loader from demolishing the wall. However, bollards may not be feasable in your case. If there is repeated abrasion on the wall, you may want to look into some type of high strength coating on the concrete surface. I used Permacoat 4000 as manufactured by chemproof (www.chemproof.com).
I hope this helps...
sounds to me like you need to talk to a structural engineer with heavy industrial experience on this one, it is not something that can be commented on accurately without actually seeing the site.
There may be other peripheral clues on the site that a more experienced eye would pick up.
The most important thing that you should be aware of as an engineer is the limitations of your knowledge.