Modifying an existing clarifier

Modifying an existing clarifier

Modifying an existing clarifier

(OP)
I am having to check an existing clarifier to see if we can add one foot of depth.  I have the existing drawings (from 1969), so I have the geometry and the reinforcing.  I do not have the design compressive strength, however, nor do I know the grade of rebar.

I plan to design a 9 ft clarifier, assuming 3 & 40 ksi (I know it's probably at least 4 ksi, but I can't be positive), and compare it to the 8 ft clarifier that is there.  Hopefully, it is still good, and all I have to worry about is detailing the wall addition.  My questions (to start with) are:

1.  Were the environmental structures requirements (ACI 350) sufficiently similar 30+ years ago to what they are today?  If not, how does one treat a conflict?

2.  Has anyone performed a similar design?  What can you recommend, and what should I be looking out for?  I know one foot does not seem like a lot, but. . . .

RE: Modifying an existing clarifier

Since you have the details for the existing (1969) design, I suggest a slight variation on your approach - try looking at the problem "backwards". Compute the hydrostatic load on the existing structure for a hypothetical 9' head and see what the stresses are in the materials. If they meet your (reasonable) minimum assumptions of 3 ksi (concrete) and 40 ksi steel - you should be ok. I'll bet that they will, too - in pre-personal computer days, most industrial type structures were conservatively designed.

www.SlideRuleEra.net idea

RE: Modifying an existing clarifier

I have done this in the past and designed the 'extension' to act as a ring beam keyed into the top of the wall.

RE: Modifying an existing clarifier

Thirty years ago, ACI 350 was nothing like it is today.  Most tanks were designed with working stress.  I believe today's load factors for durability and fluid pressure make today's designs more conservative.  On top of that, your fluid loads will increase by 27%(9/8 squared).  I'd be careful.  Also, in those days, the development length for horizontal wall bars was often not increased by the reinforcement location factor.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources