We have a Blowdown system from storage drums in Propane service in case of fire contingency to
alleviate the concerns of BLEVE (boiling liquid-expanding vapor explosion).
What will happen, if I were to blowdown from the Propane Storage Drums? We have 3 Propane drums close together and one is at 180 psig/100 DegF and the other two are at 300 psig/100 DegF. How will the autorefrigeration effect will come into play under fire conditions? Will it be mixed
vapor/liquid blowdown and at what temperature?
alleviate the concerns of BLEVE (boiling liquid-expanding vapor explosion).
What will happen, if I were to blowdown from the Propane Storage Drums? We have 3 Propane drums close together and one is at 180 psig/100 DegF and the other two are at 300 psig/100 DegF. How will the autorefrigeration effect will come into play under fire conditions? Will it be mixed
vapor/liquid blowdown and at what temperature?





RE: Propane Blowdown under Fire conditions
If the safety valves on the Propane Storage drums are sized properly for the relief under Fire contingency, is it necessary to have the propane blowdown system? What is the current practice in newly designed Lubes Deasphalting/Propane Dewaxing Units?
RE: Propane Blowdown under Fire conditions
Under what section of NFPA 58 are you following? The refrigerated container section does not seem to mention blowdown of vessels but there two paragraphs dealing with pressure relieving capacity in the events of loss of refrigeration and of fire exposure. My NFPA 58 edition is 2001.
One question, is the propane at 180psig/100 F refrigerated and compressed to 300psig/100F?
RE: Propane Blowdown under Fire conditions
These are horizontal storage drums with design pressure of 250 and 350 psig resp. Propane is stored in compressed form with both liquid/vapor phases. One drum stores propane at 180psig/100F and the other two store at 300psig/100F.
RE: Propane Blowdown under Fire conditions
Assuming the PSV's to be located at the tops of the vessels, they will pass only vapor. It doesn't matter how much of the vessels contains liquid, because there will always be vapor spaces at the tops.
If a fire occurred under a vessel (often referred to as a propane "bullet", but don't call it a "tank"), it would heat to the temperature where the saturation pressure equals the PSV setpoint. The PSV would then pop. If an equilibrium condition developed wherein the vapor generated by heat input matched the vapor passing through the PSV, the temperaure would continue to match the fluid's saturation pressure. Auto-refrigeration effects would be overcome by the heat gained due to fire.
I hope that clarifies your situation. If not, write back and I'd be happy to supply additional details.
Doug
RE: Propane Blowdown under Fire conditions
If the liquid is a mixture then the temperatire will increase as the lighter fractions boil off.
Best regards
Morten