Power calculations
Power calculations
(OP)
I was wondering if I have the ratings for a motor @ full load, say 106 Amps @ 230 V (60 Hz), and I measure that we are using 26% (around 27 Amps) of the full load amps, can I take that percentage and apply it to my original full load KWh calculations? This is for a cost savings project.
Thank you in advance.
Thank you in advance.





RE: Power calculations
At lower power levels and with slow motors, you need to consider the presence of no-load magnetizing current which is in quadrature with load-component of current (add by SRSS). The load-component varies with linearly with load and the no-load component is constant regardless of load.
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: Power calculations
RE: Power calculations
I_FL = 100A.
I_NL = Imagnetizing = 25A
You measure Imeasured = 60A
Question: What is the actual load
Model: I = I_magnetizing^2 + P * ILoad^2
where P is fraction of output horsepower 0 to 1.
Call ILoad at full load = ILoadFL
ILoadFL = sqrt(100^2 - 30^2) = 96.8 A
Call ILoad at the time of measurement ILoadMeas
ILoadMeas = sqrt(60^2 - 25^2) = 54.5A.
P = ILoadMeas/ILoadFL = 54.5 / 96.8 = 56 % of full load.
The above answer is better than using straight ratio of measured current (60/100) and good enough for most purposes but still includes a few approximations.
The tough part will be determining no-load current. If you have run the motor uncoupled and measured current, that is the no-load current. Otherwise you have to estimate (guess). For 2-pole motor maybe I_NL = 20% of FLA. For 6-pole motor maybe 30%. 20-pole motor maybe 50%
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: Power calculations
Model: I = sqrt(I_magnetizing^2 + P * ILoad^2)
=====================================
Eng-tips forums: The best place on the web for engineering discussions.
RE: Power calculations
Let's say
I_FL = 100A.
I_NL = Imagnetizing = 25A
You measure Imeasured = 60A
Question: What is the actual load
Model: I = sqrt(I_magnetizing^2 + P * ILoad^2)
where P is fraction of output horsepower 0 to 1.
Call ILoad at full load = ILoadFL
ILoadFL = sqrt(100^2 - 25^2) = 96.8 A
Call ILoad at the time of measurement ILoadMeas
ILoadMeas = sqrt(60^2 - 25^2) = 54.5A.
P = ILoadMeas/ILoadFL = 54.5 / 96.8 = 56 % of full load.
The above answer is better than using straight ratio of measured current (60/100) and good enough for most purposes but still includes a few approximations.
The tough part will be determining no-load current. If you have run the motor uncoupled and measured current, that is the no-load current. Otherwise you have to estimate (guess). For 2-pole motor maybe I_NL = 20% of FLA. For 6-pole motor maybe 30%. 20-pole motor maybe 50%
=====================================
Eng-tips forums: The best place on the web for engineering discussions.