phase monitor

phase monitor

phase monitor

(OP)
in a typical 230vac 3-phase circuit with a motor contactor and overload and disconnect, where is a 3-phase monitor generally placed in relation to these items?  I would guess before the disconnect, but I've guessed before on things.

RE: phase monitor

I usually place it after the disconnect and before he contactor.

RE: phase monitor

You want it where it can prevent the contactor from ever closing if the power is bollixed up.

So as thewellguy sez.

Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com

RE: phase monitor

There are some nice power monitors used by the refrigeration industry. Some models include three phase voltmeters, recording of the last 25 faults, phase reversal, phase loss, voltage unbalance, timing functions appropriate for a hermetic compressor, and additional connections on the load side of the contactor to detect open or high resistance load contacts.
respectfully

RE: phase monitor

(OP)
cool thanks.....I leftit in before the contactor on the input basically because it fit nicely in my drawing there :)

Thanks for the comments!

Mark

RE: phase monitor

There is an argument to be made for putting it ahead of the disconnect switch (with it's own separate disconnect and fuse protection). If the starter disconnect / breaker is interlocked with the enclosure door, the monitor may record every door opening as a phase loss (depending on it's internal power supply configuration). If you have one that does not have a fault buffer, you may lose the trip indication when you open the door to read it.

JRaef.com
Eng-Tips: Help for your job, not for your homework  Read FAQ731-376 pirate

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources