Centrifugal R-134a Air Conditioning Unit

Centrifugal R-134a Air Conditioning Unit

Centrifugal R-134a Air Conditioning Unit

(OP)
Hello all,

I have a 200 ton unit designed for chilled water at 720 gpm and 44F supply.

What happens to the compressor power consumption/efficiency if I increase the flow to 900 gpm but keep the same load and supply temperature?

Simply put, from a kW/ton perspective is it better to have a higher inlet(return) temperature and lower flow? (Assuming UA of the evaporator is constant)

Thanks in advance

RE: Centrifugal R-134a Air Conditioning Unit

I think the proposed plan is less efficient within the chiller unit itself.  The evaporator is now transferring heat from a cooler fluid incoming at a smaller delta-t to the refrigerant.  So less heat transfer driving force with a greater mass-flowrate to cool.

Aside from addressing the other issues relating to pushing 25% excess flow through a chiller, Your system efficiency will also be reduced:  You are pumping more water through the system, your end-user equipment delta-t's are reduced, and your system pressure is higher - particularly in your chiller.

RE: Centrifugal R-134a Air Conditioning Unit

If you pump in more water, the delta T reduces - the chiller is probably designed to a particular capacity and can't give more than that.

Q = m Cp Delta T.

If "m" goes up, Delta T come down.

HVAC68

RE: Centrifugal R-134a Air Conditioning Unit

(OP)
I think my question was misleading so I will re-phrase.

I understand that I have decreased overall efficincy because the chill water (CW) flow and pumping power is greater than the design flow for the given load.

I am trying to build a case to add a heat exchanger with a much greater temperature rise than that normally seen with an HVAC cooling coil.

I have power consumption curves for varying condenser cooling water inlet and CW outlet temperatures.  But I don't have any for varying CW inlet temperature.

If the evaporator is designed for an average (CW)temperature of 47.35 F with an exit temperature of 44F what happens to power consumption if the CW inlet (and average) temperature is increased for the same load?


RE: Centrifugal R-134a Air Conditioning Unit

I think my original reply addressed this.  You are raising your Chilled water return temperature with a given CHW supply temp.  Efficiency will be reduced - the heat exchanger has to do the same amount of effort with a reduced delta-t.

Chillers also reduce efficiency for both increased Cond water supply temp and reduced CHW supply temp.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources