I have a 100 foot diameter tank which holds water and we are requiring the contractor to place the slab for the tank in 4 sections (around 2000 square feet). They have come back requesting to place the slab in one pour. Our concern with one pour is the greater chance of shrinkage cracks.
As a question to other engineers, is 2000 square feet pour seem typical for a water containing structure? Is there something in the code or other documentation that I could throw back to the owner?
As a question to other engineers, is 2000 square feet pour seem typical for a water containing structure? Is there something in the code or other documentation that I could throw back to the owner?






RE: concrete slab pour limits
RE: concrete slab pour limits
RE: concrete slab pour limits
RE: concrete slab pour limits
www.SlideRuleEra.net
RE: concrete slab pour limits
How much reinforcing are you using in the slab? With the proper amount of reinforcing, this size of a pour is very doable.
Using around 0.5% area of steel I have had warehouse floor pours considerablly larger than 10,000 SF. Have done paving 'lanes' in other warehouses that were in the order of 400' long (x 10' to 15' wide) with very few hairline cracks.
Also, look into the concrete mix. Keep the w/c ratio as low as possible. There are also additives the can compensate for the concrete shrink, those these may be fairly pricey.