Cable Trays in Class 1 Div 2 area

Cable Trays in Class 1 Div 2 area

Cable Trays in Class 1 Div 2 area

(OP)
I'm having a heated discussion on this. The question is if I am using cable tray, and Type TC cable, is there some special sealing required at the boundary between the Class 1 Div 2 area and the non-hazardous area.  My take is "No" if it's ladder tray, and I don't know what happens if its solid tray. The only sealing is at the enclosure the cable terminates at.  Any opinions or links to discussion areas.

RE: Cable Trays in Class 1 Div 2 area

Take a look at NEC 501.15 and be prepared to mull over it for awhile.  There are many factors at play depending on your specific situation.

RE: Cable Trays in Class 1 Div 2 area

Section 501.15 is the right general reference, but 501.15(E)(1) and (3) is what you want to look at specifically.

A couple of things to note:

1. Cable Tray is not a raceway per the NEC (it's a support system).

2. UL's standard on Type TC says it has a "gas/vaportight continuous sheath," but is silent on whether it can transmit gases through the core. Assume it can. This is largely irrelevant to the OP, since a boundary seal isn’t mentioned in Subsection 501.15(E)(3).

3. In fact the only mention of a boundary in Subsection 501.15(E)(4) which doesn’t apply to Type TC.

RE: Cable Trays in Class 1 Div 2 area

(OP)
Thanks.  You have basically agreed with my interpretation and provided the missing link I did not have that UL 1277 says Type TC cable is gas/vaportight.

RE: Cable Trays in Class 1 Div 2 area

The issue is about fire class and additionally, as you mentioned, between hazardous and non-hazardous area. The requirement is "penetration MUST be sealed according to the intergrity of the boundary no matter ladder or solid tray is used".Generallry cable trays are terminated 100-300mm from the penetration ends depending on the size or group of cables.
There are some method in sealing of penetration;
a)Using a water base hardening compound, ex APEX
b)Using an MCT
c)Using an inert-heat activated sealant, ex RISE System manufactured by Belle Corp.

RE: Cable Trays in Class 1 Div 2 area

No need to seal.  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources