Hallo to everybody.
Please, can anybody tell me if there are optimal pressure drops in a condenser and an evaporator as a function of different refrigerants ?
Is there a preferable circuit disposition depending on refrigerant type (ex: R407-C, R410A)...

thanks in advance for your help

RE: optimal refrigerant pressure drop for condensers and coolers

Hi

In the litterature you shoulf find graphs showing for each type of refrigerants :

temperature drop at the suction gauge=f( pressure drop) for different evaporating temperatures.
This should help you decide what pressure drop you can allows in your circuit.

Rgds

RE: optimal refrigerant pressure drop for condensers and coolers

MrReds:

Your query is vague and not specific enough.  You don't state your concern (if you do have one) and what you identify as a problem area or a hazard.

There is nothing specific about the word optimal.  The "best" pressure drop is the one that works for your application.  If you want to optimize, you should study the effects of reducing the pressure drop(s) - such as more capital costs due to larger equipment, more maintenance, etc.

There are definite hazards involved in applying excessive pressure drops across evaporators when using hydrocarbon refrigerants - such as propane, ethylene, etc.   This should be an obvious deduction to users.   A below-atmospheric suction pressure at the compressor's suction flange will induce the migration of air (& oxygen) into the refrigerant's circulating system - principally through gaskets, etc.  This is a hazzard because the subsequent compression of refrigerant+oxygen raises the mixture's temperature to a level where you could get a combustion reaction.   You don't want to go there.   That's why the vaporizer's pressure (& temperature) are kept at a level that ensures that the compressor's suction pressure will always be gauge-positive.  The need for purging the accumulation of non-condensables should serve as a hard reminder of the fact that all refrigeration systems suck in air - through time and sooner or later.  It just happens and it should be addressed.

There isn't the same concern for the condenser since it normally always operates at relatively elevated pressure and the leakage is normally always outwards.

I don't know what you mean by "a preferable circuit disposition".

I hope this helps address your concern.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources