Wye Wye Transformer connection Pros and Cons
Wye Wye Transformer connection Pros and Cons
(OP)
Hi guys...I´m looking for some information (technical or personal) that be related with the pro´s and con´s to use the Y Y transformer connection in comparison with the other ones.......anyone can help






RE: Wye Wye Transformer connection Pros and Cons
IEEE guide for application of transformer connections in three-phase distribution systems
ANSI/IEEE Std C57.105-1978
Abstract
This guide concerns transformer connections in 3-phase distribution systems. Distribution systems are characterized by primary voltages up to and including 34.5 kV, usually have a preponderance of connected transformers with low-voltage windings below 1000 V and furnish electric service to consumers. The characteristics of the various transformer connections and possible operating problems under normal or abnormal conditions are treated. All combinations of Delta and Y, grounded and ungrounded, T connected, zigzag, and certain special connections are considered. Only two-winding transformers are included.
RE: Wye Wye Transformer connection Pros and Cons
http://s
RE: Wye Wye Transformer connection Pros and Cons
RE: Wye Wye Transformer connection Pros and Cons
What application do you have? Wye-Wye are mostly used by utiltiy companies mainly for two reasons. One is the groundind as inidcated in IEEE green book, that allows them to ground the grid at more points.
Also utility grid could have generation on either side of the transformers, so wye-wye provides convenient point of grounding the neutral at source, regardless of which direction the power is flowing.
Other is cost. I beleive wye-wye costs little less than a delta-wye or delta-delta? May be due to difference in insulation as wye-wye coils need insulation for L-N voltages. Don't really know.
If you are an end-user and your application is generally unidirectional, I would use dela-wye. Wye being the secondary (user) side. It is most common configuration. I would not use any other configuraiton unless it is somehow required otherwise.
RE: Wye Wye Transformer connection Pros and Cons
Wye-Wye transformer connections should generally be avoided because of the objectionable characteristcis of such connections.
First, a connection of this type generally requires that the primary neutral point of the transformer windings be connectged to the neutral of the source. Without this connection of the prumary neutral, unbalanced loading from phases to neutral on the secondary side produces a " floating neutral" on the primary side, with a serious unbalancing of secondary wye voltages and reduced power handling capacity.......
The second, and major, objection to the general use of wyr-wye connected transfoermers arises from the character of the harmonic current genreated in such a hookup........
RE: Wye Wye Transformer connection Pros and Cons
RE: Wye Wye Transformer connection Pros and Cons
Cost might be an issue, especially on the higher voltages. Normally windings subjected to a voltage of 66kV and higher are connected in star, because, in a star-connection, the winding isolation can be degraded towards the neutral point. But usually the lower voltage side will be connected in delta and a grounding transformer will be used to create a grounding point.
It depends on your application, but I would rather try to stay away from star-star transformers due to protection and harmonic issues. Why would you want to use a star-star transformer?
Regards
Ralph
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
RE: Wye Wye Transformer connection Pros and Cons
The only other reason would be if you need to be able to pass zero-sequence current through the transformer for some reason.
If establishing a ground source for the system is the issue consider adding a separate zig-zag transformer and grounding resistor.
RE: Wye Wye Transformer connection Pros and Cons
In the US, wye-wye pad-mounted transformers have become the norm for a lot of utilities serving commercial customers, at least out west where I am.
The transformers are a little cheaper because the primary winding can be graded and it eliminates supposed risk of ferro-resonance when single-phase switching or fusing is used upstream.
When my client is on the secondary side, I generally push for a delta-wye transformer for all the normal reasons.
RE: Wye Wye Transformer connection Pros and Cons
"the utility connects single-phase loads line-to-ground"
Are you refering to SWER-lines?
dpc:
After reading again through the answers I noted jghrist also mentioned ferroresonance. I have not thought about it previously, but it makes sense. Thanks. At least we all agree on using a delta/star connection, if possible, most of the times.
Regards
Ralph
Failure seldom stops us, it is the fear for failure that stops us - Jack Lemmon
Make the best use of Eng-Tips.com
Read the Site Policies at FAQ731-376
RE: Wye Wye Transformer connection Pros and Cons
"At least we all agree on using a delta/star connection, if possible, most of the times."