Confinement of serviceability compression reinforcement in beam
compression reinforcement is sometimes provided in beams solely for the purpose of reducing time-delayed deformations due to creep and shrinkage of concrete. Does this reinforcement need be confined (with ties)?
What rules govern the termination points of such compression reinforcement?
RE: Confinement of serviceability compression reinforcement in beam
I don't know if you are designing under the ACI 318 code or not. For ACI, they require that all compression reinforcing in beams be enclosed with ties or stirrups which satisfy Section 7.10.5. This section requires the following:
For longitudinal bars of #10 or smaller, the ties may be #3 bars. For longitudinal bars larger than #10, the ties must be #4 bars or larger.
The spacing of the ties cannot be greater than 16 longitudinal bar diameters, 48 tie bar diameters, or the least dimension of the member.
The compression ties must be provided throughout the distance wherever the compression longitudinal bars are required.
There's a bit more in section 7.11 that you should read. I