HV & Control cable segregation

HV & Control cable segregation

HV & Control cable segregation

(OP)
I appreciate your help.I'm installing an underground 11kv feeder (2KM long) and two control cables for the inter-trip send and receive signals from Multilin relays. What is the minimum segregation required between the two? I have seen some thing from 150mm to 1500mm? Could someone help please? Best Regards,

RE: HV & Control cable segregation

I'd look at using fiber optic for the transfer trip, then you won't have interference worries.

RE: HV & Control cable segregation

(OP)
thanks davidbeach, I thought in this solution, but as I do not have good experience with such cable for protection, I prefer to use normal cable. The other thing of course is the cost?

RE: HV & Control cable segregation

In the petrochem industry we tend to specify 300mm min.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources