Is there any literature out there that address conduit or pipe embedded in composite concrete slabs? Electricans here argue that they do it all the time, but I'd like to get something in writing to prove them wrong.






RE: Conduit and Pipe in Composite Slabs
RE: Conduit and Pipe in Composite Slabs
Conduit embedded in any type of concrete member is perfectly fine and covered in Section 6.3 of ACI318. There are some restrictions about the location, spacing, maximum percent of the area of the cross section, etc. Just make sure they are not using aluminum conduit.