Cleaning High Voltage Lightning Arresters
I'm new to eng-tips and was just hoping for a little help on finding a link for cleaning High Voltage Lightning Arresters. Any info would be greatly appreciated.
RE: Cleaning High Voltage Lightning Arresters
You will find standards for maintenance of arrestors there. A more specific question will get you a more specific answer. There are some great minds with alot of experience here.
Scott Peterson
Training Manager
Power Plus Engineering
www.epowerplus.com
Or are you looking for methods of cleaning while the equipment is energized, such as corn cob blasting?
I would also check the tightness of all connections, including the base bolts and look for signs of overheating. If these are large LA's, they could be Doble testing at the same time the transformer and transformer bushings are. The LA's on the transformers can be cleaned the same way the transformer bushings are.
Hope that helps.
For developing a RCM program you really should download the NETA MTS, it tells you how and when to conduct PM on power systems. You can also reference the 2006 NFPA 70B.
You can reach Collinite at 315-732-2282 (Happen to have can on my desk now)!
ht
Check if the enclose test could guide you:
Describe your actions sequentially to restore the station (temporarily and permanently)
Inspect the potential device insulator for sing of flashover and other damage damages such as insulator puncture, crack in the porcelain, oil leak or any other physical damages
If not damage is found, proceed to clean the potential device with water followed by a wipe down with isopropyl alcohol to remove any dust or salt deposit.
After the cleaning, the system the system is ready to be restore and get the line back in service
For longer term, there are several options available to protect the potential device from flashover:
o Water washing.
o Surface coating such as silicon grease, high resistance glazing, hydrocarbon grease, room temperature vulcanizing (RTV), etc.
o Install corona ring the made uniform the voltage distribution along insulator.
o Replace the unit with higher-leakage insulator or no ceramic insulator unit.
Due to the variety of options and methods a study is recommended to determine include a live cycle cost of best protective action to maintaining the expected level of reliability and system availability.
The need for cleaning arrester/insulator depend on the frequency and risk level of flashover that is directly associaty with pollution level, contaminat deposit, environment conditions, lightning activity, overvoltage, creepage distance etc.
If there is severe problem of contamination/flashover, the enclose link may have application: ht