Need info on SSR advantage for 220 vac contorl
Need info on SSR advantage for 220 vac contorl
(OP)
Hello;
I need to control a 220 VAC Inductive Load from a TTL/CMOS control.
I always thought that SSRs were designed for this task. But, a co-worker says a mechanical relay driven by a ULN2003 or IRF511 and controlled by TTL/CMOS, would do just as well. I think the mechanical relay solution is very risky.
I need info on the SSR advantage.
Thanks.
I need to control a 220 VAC Inductive Load from a TTL/CMOS control.
I always thought that SSRs were designed for this task. But, a co-worker says a mechanical relay driven by a ULN2003 or IRF511 and controlled by TTL/CMOS, would do just as well. I think the mechanical relay solution is very risky.
I need info on the SSR advantage.
Thanks.





RE: Need info on SSR advantage for 220 vac contorl
No spart, less HF radiation.
MINUS: less forgiving about overload, momentary OL
can kill it.
MR: PLUS: can tolerate/survive momentary overload
MINUS: limited life-time, more power to drive it.
Sparking causes more HF.
Plesae read FAQ240-1032
My WEB: <http://geocities.com/nbucska/>
RE: Need info on SSR advantage for 220 vac contorl
http://ww
----------------------------------
Sometimes I only open my mouth to swap feet...
RE: Need info on SSR advantage for 220 vac contorl
The typical failure mode of an SSR is shorted output - it won't turn off.
What happens to your inductive load when you can't turn off the power?
Thanks, Scotty, for the link. Excellent summary.
Dan
RE: Need info on SSR advantage for 220 vac contorl
But, I need to know about driving large AC inductive loads from a TTL/CMOS logic control signal.
I thought that leakage currents were more likely in a mechanicl relay. And the leakage currents, even if buffered by a ULN2003, or IRF511, could work their way back to the TTL/CMOS circuit, and zap it.
Even if SSR and Mechanical Relays are equal in safty. I like the SSR for the simplicity of circuit connection.
Thanks again, in advance
RE: Need info on SSR advantage for 220 vac contorl
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Need info on SSR advantage for 220 vac contorl
Either the mech relay or the ssr will offer isolation from the final 220vac inductive load and your control (ttl) circuit.
There is some leakage current between the ssr and the final load. But that should not impact the ttl part of your circuit.
RE: Need info on SSR advantage for 220 vac contorl
the relay's coil becomes a secondary of a psudo-transformer.
The AC current could find a path from the relay coil, back to the TTL/CMOS source and zap it.
I thought that such a condition would be happen with an SSR.
So, for this large AC inductive load, am I safer with the TTL/CMOS driving an SSR?
RE: Need info on SSR advantage for 220 vac contorl
Now improper layout and ignoring the inductive kick of the relay's coil will cause you problems. The standard solution is to put a diode across the DC coil (parallel) to it but in the non conducting direction (when energizing the relay).
Mechanical relay's are generally much less expensive then SSRs, and provide no heating issues. SSR's can have serious heating issues and are lossy (have a voltage drop) whereas mechanical relays can be considered to have no losses(in most cases).
Unless you have a rapidly switching application or need the zero current switching of an SSR they often don't make much sense. As previously mentioned SSR's don't even work with large inductive loads but are often destroyed by them.
We can give you more info if you describe your application in more detail. What load? What switching rate? What's controlling the relay?
Keith Cress
Flamin Systems, Inc.- http://www.flaminsystems.com
RE: Need info on SSR advantage for 220 vac contorl
Paul
RE: Need info on SSR advantage for 220 vac contorl
JRaef.com