Concrete anchoring
Concrete anchoring
Concrete anchoring
I am trying to select a concrete anchor to hang a post (hanging vertically downward). The post have a square flange on the top with mounting hole.  My attempt is to use a heavy bolt to fix the post to the ceiling.  I have done a dynamic analysis, it shows the resonance frequency is in the neighbourhood of 400 Hz, which is within the vibration test range.  The dynamic force is about 2000 lb (share by 4 bolts), with the static load (weight) of 50 lb.  I, then, used the concrete anchor datasheet and found a anchor which is  3/8 thread.  The pull out strength is 5300 lb. Assuming the bolt itself can support the dynamic load.  3/8 threaded concrete anchor seems to be more than enough for the job.  Can anyone confirm my result?   (I am no expert in concrete stuff).  Note: Please ignore the stress cone effect between bolts as the bolts are spread apart widely.
RE: Concrete anchoring
I typically don't use anchors less than 1/2" dia... and with 8" embedment, they are more than adequate for your loads.  You mention dynamic analysis... Concrete has a very weak tensile capacity and you might check to see if it's possible to generate a fatigue tensile failure....
dik
I don't like to use wedge or expansion type anchors for any kind of vibratory situation.  Since they work by crushing a small zone of concrete, I worry that the zone might progress and work loose.
Even though they didn't have a good experience with the big dig epoxy anchors (thread507-159632) in an overhead orientation, that's what I would use.  Or undercut anchors, even though will have substantial overkill for your loads.  Note that you should use ICBO allowables as opposed to published catalogue values.