Condesate traps in compressed air lines?

Condesate traps in compressed air lines?

Condesate traps in compressed air lines?

(OP)
Guys,

Do we need to provide condensate traps in the compressor ring mains when the compressed air has achieved a dew ppoint of 3C or less either thru a refrigerant dryer or a dessicant dryer?I was told by some one they are not required as there is very little moisture left in the air leaving the dryer.

Thanks for your feedback.

RE: Condesate traps in compressed air lines?

If the temperature goes below 3ÂșC, you could still condense more.  How much more?  What's the lowest temperature you'll have?

   Going the Big Inch! worm
http://virtualpipeline.spaces.msn.com

RE: Condesate traps in compressed air lines?

Your air may leave dry, but every leak and or entry point to the system has the potential to diffuse moisture back into the line.  If it has very far to go, and/or your system doesn't have good tightness, you will need the traps.

Do an advanced search on this site.  The topic of moisture diffusion was discussed in some detail a few years ago.

rmw

RE: Condesate traps in compressed air lines?

If you mean 30C is pressure dew point and if the pressure is minimum 7 kg/cm2, my experience is that you need not put traps. This corresponds to about -200C ADP. Nevertheless, the minimum possible ambient temperature should be not less than your atmospheric dew point.

Guidelines by Health and Safety Executive say to install traps for each and every uprising main. When we had been through BSC audit, I did the modification for the existing lines. I never observed any moisture being drained. Leakage became a nuisance and I replaced all the traps by manual valves.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources