Deflection improvement For the Existing Shed
Deflection improvement For the Existing Shed
(OP)
Hi Fellows
A urgent question. I designed a factory shed last year, and they are building it now. The rafter is 310UB slope from one end to another, span 20m, with 3m haunch both end. The column is 360UB, high 3.6m at on end, and 5.2m at the other. The rafter rigid connected to the column. There is a bolted splice at the middle of the rafter. (top and bottom flange, web bolts with plate).
Now my problem is, in my calculation, the rafter is deflect 43mm under dead load, but now during constrution, the beam is deflect 30mm only under self weight, So I guess it will deflect more than 80mm under deal load (included purlin and roof sheeting). The owner is not happy about this deflection. Do your guys have any idea to improved the deflection without major change of the design? I think the main reason for this happen is because the bolt splice, in my member design, I consider it as a single beam, but because 310UB not available for 20m long, so I designed a bolt splice at the middle, may be the bolt hole and the bolts create some rotation.
Thank you for your time.
PowerRanger
A urgent question. I designed a factory shed last year, and they are building it now. The rafter is 310UB slope from one end to another, span 20m, with 3m haunch both end. The column is 360UB, high 3.6m at on end, and 5.2m at the other. The rafter rigid connected to the column. There is a bolted splice at the middle of the rafter. (top and bottom flange, web bolts with plate).
Now my problem is, in my calculation, the rafter is deflect 43mm under dead load, but now during constrution, the beam is deflect 30mm only under self weight, So I guess it will deflect more than 80mm under deal load (included purlin and roof sheeting). The owner is not happy about this deflection. Do your guys have any idea to improved the deflection without major change of the design? I think the main reason for this happen is because the bolt splice, in my member design, I consider it as a single beam, but because 310UB not available for 20m long, so I designed a bolt splice at the middle, may be the bolt hole and the bolts create some rotation.
Thank you for your time.
PowerRanger






RE: Deflection improvement For the Existing Shed
Also, you mentioned that you rigidly connected the rafter to the column. When you calculated deflection, did you consider that the column will rotate?
If you calculated the deflection in the member properly, and the deflection is greater than that, something else is going on. It is up to you to figure out what that something else is.
RE: Deflection improvement For the Existing Shed
RE: Deflection improvement For the Existing Shed
I have had a similar case previously and we jacked to correct the deflection, then we loosened the bolts and jacked another 30mm. Following retightening the bolts we welded around the splice plates.
The question is whether to wait until all the deadload has been applied and then to carry out the correction. This may provide a more accurate final result.
RE: Deflection improvement For the Existing Shed
For a 305x102x25UB (which is admittedly the smallest) the maximum deflection considering a simply supported member is 57mm and considering fully fixed is 11.4mm under dead weight alone.
Now because you have a stanchion with 'x' stiffness and a column with 'y' stiffness you are going to have some rotation at your haunches, so I would expect a deflection somewhere between these values.
Your span to depth ratio is about 65 which is quite high. A rule of thumb I have come across is between 35 and 45 for estimating purposes. Is it possible the frame is just not stiff enough?
RE: Deflection improvement For the Existing Shed
Hi Ussuri, the second moment of area of my UB is 86.4X10^6 mm^4. If you consider the span between haunch, it will be only 14m, which will give a 45 span to depth ratio.
Hi Tomfh, Zambo, Jacking the rafter up and re-treat the bolting splice can help, but need to jack up not just the mid span, (because the rafter will sag between the column and the jacking point, so at least 2 more jacking point in between is required).
But anyway, the owner agree to "suffer" this happening. But one thing he mentioned, and make me feel that not sure right or wrong. He said, if we know the rafter will sag at the design stage, why did we not design the rafter with greater pitch, than, when it sag, it will come down to the pitch he want. He get his point, but one thing make me not sure is, later, does the drawing from the architect, shows the pitch of th rafter, should I consider it as the final pitch in my design, or the initial pitch (which used in the model).
Thank you.
RE: Deflection improvement For the Existing Shed
RE: Deflection improvement For the Existing Shed
Comments on a number of points;
-"the beam is deflect 30mm only under self weight, So I guess it will deflect more than 80mm under dead load"; This is not necessarily true; fabrication/bolting/joint slip could all have contributed to the initial deflection and possibly won't contribute (much) to additional deflection.
-"Is the splice designed with HSFG bolts or as a simple connection? Are the mating surfaces of the joint painted? "; Good questions, bolts must be grade 8.8/TF and properly tensioned, and either no paint, or compatible primer, under the splice plates.
-"I have had a similar case previously and we jacked to correct the deflection, then we loosened the bolts and jacked another 30mm. Following retightening the bolts we welded around the splice plates."; Good advice
-" Is it possible the frame is just not stiff enough?"; I would ask the same; my rule of thumb is 19-20mm per metre span, 15mm is low.(I'm not saying it isn't correct, however it is at the light end)
-" but need to jack up not just the mid span"; I don't see why, you are only correcting (or preferably over-correcting) the rotation across the splice.
-"why did we not design the rafter with greater pitch"; Yes, it is common for long span beams such as this to be designed with a pre-camber or pre-set to counteract dead load deflection. For lower pitch roofs dead load defl'n such as this could cause ponding and leaks.