(OP)
Does anyone have some background on the 1.3 reinforcement location factor for horizontal reinforcement placed with more thna 12" of fresh concrete below the development length or splice?  The code only comments that the factor was changed to 1.3 from 1.4 in 1989 but gives no reasoning for the need for the factor or why this condition requires additional development.

RE: Development Length Location Factor

From MacGregor's textbook: "During the placement of concrete, water and mortar migrate vertically through the member, collecting on the underside of reinforcing bars.  If the depth below the bar exceeds 12 in., sufficient mortar will collect to weaken the bond significantly."

RE: Development Length Location Factor

Just a small bit of additional description to correlate with Taro - imagine a horizontal bar and the concrete sags a bit after placement - you have a small bit of void under the bottom of the bar and thus, the circumferntial bond on the bar is reduced a bit.

RE: Development Length Location Factor

What a good post!  This is one of those questions I've been wondering about and never remember to ask.  

RE: Development Length Location Factor

Prior to 1989, this requirement was stated in the code as a requirement for "top bars".  At some point, the reference to "top bars" was removed to clarify that this is required for all horizontal bars, such as horizontal bars in retaining and foundation walls.

RE: Development Length Location Factor

The reason it doesn't apply to bottom bars is because the hydrostatic weight of the wet concrete ensures there is sufficient compaction of the concrete at this level to ensure adequate bond.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources