building air exchange rate
Can someone help me with a solid reference to usual and customary engineered air exchange rates for large buildings. I'm a health physicist trying to defend what I think is a reasonable exchange rate of 10/hour to a regulatory agency. This is the case for the building as now engineered. Is there any credible scenario where the building would be used and would not have such an exchange rate? What is the normal range for commercial buildings?
Harry Newman
Harry Newman
RE: building air exchange rate
There is a regulation to what should be the maximum CO2 percentage in the air.
Based on this calculation it was derived that 16 cfm fresh air is required per person.
If you are taking fresh air from outside always 10ACPH can be high.
As it is difficult to put the formula here I can forward it to you if I have your e-mail id.
The building is currently a R&D lab with hoods in every roon. The actual exchange rate currently is 10/hour. I am getting called on the possibility that some time in the future the bldg may not be used for the same function and therefore have a lower exchange rate (this affects the modeling work I am performing for residual contaminants).
I really need something hard I can point the reviewers to.
Harry
Also, ASHRAE 62 establishes design criteria for outside air based on occupancy, and estimates 7 people per 1,000 ft2, with a minimum 20 cfm of outside air per person. Do the math and this only gives about .9 ACH of outside air.
In general, a certain air exchange rate is less of a "need" than the result of the HVAC systems doing what they need to do. There are, however, certain ACH requirements for certain facilities (per AIA - such as 6 total ACH for x-ray rooms). Put a lab hood in that x-ray room and you'll probably get over 20 ACH resulting from the volume of hood exhaust. 5-7 ACH total might typically result from normal, office-type space conditioning.
Hopefully this helps some.