Can anybody suggest a design computation of a transformer room ventilation (forced air) with the following data?

Transformer area - 4.00m(L) x 3.00m(W) x 4.00m(H)
Location - at the side of the building
Transformer size
   1000kVA, 13.8/0.415kV, 60hz
   iron losses - 1,800 watts
   copper losses at nominal load - 12,100 watts
Ambient Temp - about 30-35 deg C

We need to construct this room.

Thanks
Arvin

RE: TRANSFORMER ROOM FORCED AIR VENTILATION DESIGN CALCULATION

I'm sure there is a calculation method available.  I would search the IEEE standards at www.ieee.org

RE: TRANSFORMER ROOM FORCED AIR VENTILATION DESIGN CALCULATION

You may get more help at the HVAC/R engineering forum.
respectfully

RE: TRANSFORMER ROOM FORCED AIR VENTILATION DESIGN CALCULATION

(OP)
thanks guys, will try to look into the ieee website and HVC forum.

regards,
Arvin

RE: TRANSFORMER ROOM FORCED AIR VENTILATION DESIGN CALCULATION

Apart from some published literature, you can find these calculations in old Brown Boveri Switchgear Handbook or in its latest editions of ABB Switchgear handbook.This handbook can be purchased through ABB website.

RE: TRANSFORMER ROOM FORCED AIR VENTILATION DESIGN CALCULATION

In case you're still working on this --

We use a "rule of thumb" of 5cfm per kVA of transformer, which is conservative, but helps account for issues that hinder the performance of the blower. This would give you a value of 5000 cfm forced air ventilation. You should place the intake and exhaust on opposite sides of the room, with intake low and exhaust high.

RE: TRANSFORMER ROOM FORCED AIR VENTILATION DESIGN CALCULATION

If you take the total heat losses into the room, (13900 Watts) and calculate the heat load at 3.4 Btuh/watt this gives you a heat load of 47,460 Btuh which at approximately 12000Btuh/Ton of cooling would require an A/C unit sized at 4 Tons of cooling.  A small split system would suffice which at the rule of thumb of 400cfm/ton would mean about 1600cfm of conditioned air.  If you have a chilled water system, you could further reduce the amount of air depending on the water temperature and if you had a dedicated VAV box for the room.

As "AllGreek2me" stated however, (and if you can ventilate the room with air at an entering temperature sufficiently low at all times of the year to maintain the 30-35 degrees C), you could do it with just exhaust and outside or precooled air, but the air volume you would have to move would increase dramatically.  5000cfm is quite conservative, but not extraordinarily so.

Best of luck.

RE: TRANSFORMER ROOM FORCED AIR VENTILATION DESIGN CALCULATION

(OP)
thanks very much to all who provided inputs!

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources