Welding Tanks to Foundation
Welding Tanks to Foundation
(OP)
I recently inspected three fuel storage ASTs in Florida, and found that all three tanks were welded to their foundation. That is, the concrete pedestal on which they stood had steel plates (probably small I beam pieces) cast into it, and the tanks were welded to those plates directly. Has anyone ever seen this, and wouldn't it be better to weld tabs to the tanks and bolt them down that way. The welded areas were poorly coated due to clearance issues and had already begun to corrode after only two months of service.
If anyone can point me in the right direction as to what Florida regulation requires tanks to be anchored, it would be helpful.
FYI, the tanks are 30K vertical tanks, covered with a metal pole barn, and surrounded with a concrete containment structure. Tanks are UL rated. Thanks
Chris
If anyone can point me in the right direction as to what Florida regulation requires tanks to be anchored, it would be helpful.
FYI, the tanks are 30K vertical tanks, covered with a metal pole barn, and surrounded with a concrete containment structure. Tanks are UL rated. Thanks
Chris





RE: Welding Tanks to Foundation
RE: Welding Tanks to Foundation
I can see corrosion being a problem here. This seems like a week connection, as it seems the uplift force could bend the tank bottom chime down. The only way I can see this working would be if uplift forces were very minimal- which is what you have with a 30,000 gallon tank.
Generally, I think building codes would require construction per the tank codes. For a UL tank, you'd need to refer to the UL standards to see if that is permitted. I don't think it would meet API-650.