Motor Starter Protector Help
I'm looking to buy an IEC rated motor starter protector(a motor circuit protector with overload protection from what  I can tell).  All I can find is the Siemens brand MSP. I'd like to find other brands, like AB, Eaton, or GE.... I've been browsing the internet and have had no luck.  Does this sort of device go by different names than motor starter protector?  Anybody know a quick and easy way to find products equal to this Siemens MSP 3RV1011-0JA10?
Tim
RE: Motor Starter Protector Help
Try thermal-magnetic motor circuit breaker as a description. Telemecanique market their GV2***, GV3*** and GV7 *** series of breakers which are a broad equivalent to the Siemens part, as are A-B's Bulletin 140M series.
  Sometimes I only open my mouth to swap feet...
Overload or overload relay.  Try looking at Sprecher & Schuh, which is now part of A-B, in fact both A-B and Cutler-Hammer market S&S overloads with their name on them.   Link:  www.ssusa.cc/
Bruce Klauba
That looks like a manual motor starter to me.
What is the intended use?
Try the search terms "Motor Protective Switch" or "Motor Circuit Protector" or "IEC manual motor starter" (use the quote marks to filter your results). Every IEC control manufacturer has them, but if you are looking at their US web sites you will find them under "manual motor starters" because that is as close as we come to the concept. They really are more than that, but for a long time UL and NEMA had no classification for them other than manual starters, so a lot of IEC suppliers called them that and it has carried on that way.
JRaef.com
Eng-Tips: Help for your job, not for your homework  Read FAQ731-376 pirate
Schneider Electric has a good line of motor starters and protectors. I use the Uline units. They are modular and have all the features you will ever need.
http://www.schneiderelectric.com
Telemecanique is under Schneider Electric as well as Square D. A thermal trip and magnetic trip rated CB's are available.
Maybe we can help...if you are in the uk
                     Jeff
               www.motors-direct.co.uk