Vacuum Breaker
3

Vacuum Breaker

Vacuum Breaker

(OP)
Are vacuum breakers required according to any code for a heat exchanger condensing steam in the shell side?

We want to install a vacuum breaker as it would protect the shell, however others say there is no requirements per code and hence not needed.

Thanks in advance.


Excuse for posting in two places!

RE: Vacuum Breaker

I've never seen any code that requires a vacuum but it's good piping practice to include one. With out one condensate is not going to be able to leave the heat exchanger when the supply steam is shut off. As the steam begins to condense the pressure in the vessel will begin to drop and eventualy go into a vacuum, not allowing the condensate to freely drain, where the damage can occur is as steam reenters the vessel water hammer can occur, you've also lost capacity of the HX while the steam is trying to drive the condensate out.

I'm not a real engineer, but I play one on T.V.
 A.J. Gest, York Int./JCI

RE: Vacuum Breaker

(OP)
Thanks Yorkman. That is the primary reason we were suggesting its use.

RE: Vacuum Breaker

And then there is the pragmatic consideration: A HX shell is basically a steel balloon, and tolerates pressure well. But one can crumple like a toothpaste tube with vacuum loads.  

RE: Vacuum Breaker

Along with the vacuum breaker might I suggest an air vent rated for steam. Think of a steam heat exchanger as a breathing vessel you need a vacuum breaker so air can be drawn in to let the condensate out and then it needs an air vent to expell the air to let the steam back in.

I'm not a real engineer, but I play one on T.V.
 A.J. Gest, York Int./JCI

RE: Vacuum Breaker

(OP)
Thanks for the good point Yorkman.

We are going to installing a vacuum breaker and air vent connections on the shell.

RE: Vacuum Breaker

Thermostatic traps are excellent air vents.

RE: Vacuum Breaker

Thermostatic traps are excellent air vents - both Watson McDaniel and Spirax Sarco make a couple different flavors designed specifically for use as air vents.  As far as vacuum breakers go, determine the CFM requirements and then the cheapest solution is to install a light seat pressure spring check valve backwards.

RE: Vacuum Breaker

Dear Sirs,
steam and air should be kept apart. I recommend you to google "heat exchanger stall steam" or simply visit http://www.spiraxsarco.com/learn/modules/13_1_01.asp.

To install a vacuum breaker is a cheap solution but you should be aware of the concequences.

rgs

RE: Vacuum Breaker

IF the operating or design GAUGE pressure of the shell side is relatively high,- Then the shell may be capable of withstanding vacuum conditions.  

IF vessel collapse or failure due to vacuum is the concern, I would check with the vendor,

Regards

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources