Outdoor Ductwork Insulation
In the project I am working on, the existing outdoor air-conditiong (heating and cooling) duct was insulated with 1-1/2" fiberglass and aluminum vapor barrier jacket. However, the insulation at the bottom of the duct always got wet after rain, and already become loose now only after a couple of years new installation.
Has anyone had similar experience or any suggestion what's the best insulation and finish for the outdoor duct?
Thank you very much.
RE: Outdoor Ductwork Insulation
Depends on how you define "best".  From the sounds of your post, there was no re-covering on the thermal insulation wrap?  IE:  It was the plain foil finish exterior finish?  The normal commercial level is one of two options:
Option 1:  Exterior thermal wrap of min. 2" foil faced duct thermal wrap rigid board insulation, with a re-covering of 0.8mm aluminum sheet, lapped and sealed weatherproof with band clamps on 600mm centres.
Option 2:  Internally lined duct insulation with the sheet metal duct as the outer surface, sealed and waterproofed.
Additional enhancements for institutional/better quality:  Use option 2 with perforated liner on the insulation, and another exterior double wrap of bituminous/asphaltic coating impregnated fibreglass cloth (which could also apply to Option 1, as well).  Then a re-covering with 0.8mm aluminum sheet for heat reflectance.
Yeah, expensive, but depends on how long you want this to last and what the energy losses are.
Thanks, GMcD. I don't quite understand what "re-covering" means in Option 1. Is the re-covering aluminum sheet in Option 1 a separate layer from the thermo insulation?
Thanks again for help.
go to armacell.com, look for armatuff
FXDFM:  yes- the re-covering is another sheath over top of the basic thermal wrap insulation.  The light wieght flexible foil finish on the duct wrap is not a weather barrier no matter how well it's installed.  You need to protect it with a real weather shield sheathing.
Thanks both of you, GMcD and AbbyNormal.
GMcD,
Could you please give me some manufacturers for the Option 2 with exterior enhancement?
There are no "manufacturers"- you have to call your local insulation contractor to do this.  Asphaltic coverings and sheet aluminum are generally available from a variety of suppliers, but if this is specifically an insulation scope, then call your friendly neighborhood insulation contractor/supplier.
GMcD, Thanks.